Has anyone actually carried out the calculation assuming a few figures that you aren’t going to know like the length the supply cable to the DNO TX? Unless your bang on top of the TX I can’t see it ever being above 1000.
CRL = Fenv /(Lp x Ng)
Fenv is an environmental factor selected according to Table 443.1
Lp is the risk assessment length in kilometres, and
Ng is the lightning ground flash density measured in flashes per square kilometre per year relevant to the location of the power line and connected structure.
Unless you can get all the above info then your going to fitting them on commercial jobs..
For domestic a get-out-clause is given for ‘single-dwelling units’ where the ‘total value of the installation and equipment therein does not justify such protection”.
For someone with just a sky box and tv, doesn’t really justify such protection. For someone that has multimedia setups, intelegent lighting controls, smart heating controls and so on it probably does justify having one fitted.
For the cost of them which aren’t massively expensive then it would be worth having a chat with the customer about having one fitted. Last house I done spent 7K on a HDMI matrix so I don’t think he would be bothered about an extra 60 quid for a SPD.