Since a few of you seemed to like my posts so much.... I’m looking at you @Spoon @marconi and @richy3333 :p

....here’s the EICR coding one out of the view of trainees if you want to have ago and a bicker about coding
None of the pics where from EICRs just normal day to day work where I stumbled across these.


8646F291-8646-4DE5-9673-0E535C20D36B.jpeg
B5570F9D-40AD-4615-86EF-316C65C9ADB5.jpeg 1405FA9D-CF99-4F27-A0D5-7F98D470C752.jpegThe next two are the same thing from different angles.8BE87ADC-986A-4799-AB82-FB390EAAEF3B.jpeg C5325B1C-083D-4D45-A08B-30FB15B5637C.jpegThis was discovered when I pulled down a down light. 68F3E0BB-69D7-4B59-B9AC-D63CD4DA80AC.jpeg26F005A5-DB16-4EB0-82D5-61265A581ED4.jpeg 6BD93F6F-0B85-4DB4-AF7A-CFDB88EADA90.jpegThis is one cable just left very very long and looped around the bottom of the box it is bonded properly though. EBE21B40-CD1D-4134-8372-B2D7A3676BD6.jpeg

5B62A86E-D8A6-4913-B2A4-12A9FA9FABD9.jpeg
 
Last edited:
Thought id check in whilst on the holidays in good old germany as i am wide awake from too much food and drink after watching tonights football in the pub. The locals are light weights on the beer but do love a good sausage.
Talking of eicrs... what you make of this in the shower room in the hotel i am in.
Plug adjacent to sink, mains voltage too. I really dislike these european plugs. Look so flimsy and cheap.
For good measure they give you a mains hair dryer too.
Not sure about german regs but thought we were all meant to be on same road.
Wouldnt do it in the UK.

20181205_231144.jpg

20181205_231208.jpg
 
Dirty bugger!
They have takeaways that sell just sausage in various ways.
Eaten them everyday so far from the xmas market. Also had it chopped up with curry sauce on top. They love it...
At lunchtimes you see them queued up to get some.
Of course that’s what you meant. You in Germany on business? Without your significant other? Curry wurst is good but dunno if it’s polish or German I know it makes me need the loo for a number 2 in a hurry though:eek:
 
Of course that’s what you meant. You in Germany on business? Without your significant other? Curry wurst is good but dunno if it’s polish or German I know it makes me need the loo for a number 2 in a hurry though:eek:
Leisure doing a but of RandR with the other. Been seeing the christmas markets and visiting friends in Cologne.
They also do this very thin pizza type thing called flammkuchen. Base is very thin and cooked in open oven for couple of minutes. Taste amazing.
I have learnt that not all german sausage is equal. Some are nasty and as for the curry sauce, it aint half as good as what we get in blighty!
 
Leisure doing a but of RandR with the other. Been seeing the christmas markets and visiting friends in Cologne.
They also do this very thin pizza type thing called flammkuchen. Base is very thin and cooked in open oven for couple of minutes. Taste amazing.
I have learnt that not all german sausage is equal. Some are nasty and as for the curry sauce, it aint half as good as what we get in blighty!
Well enjoy ;)
 
OK, I'll be first to have a go! As some of you know, my experience lies in temporary event power systems (hence the avatar) so please be gentle where I've missed things or misidentified something glaringly obvious to those with the domestic experience I don't have. FWIW I'm planning on tackling 2391-52 next year, so any comments will be helpful.

Busbar internal finger cover missing – C1

Blanking plates missing – C1
CPDs not identified – C3

Evidence of heat damage/burnt loose cable – FI / C1

Modified RFC+spur tails/joint – FI

Omission of sleeving on mixed old & new colours (& check there is a notice at the CU)– C3

Terminal block & earth not continued to lighting fixture (may or may not be required, fixture dependent) – FI / C2

Poor dimmer terminations / incorrect identification of CPC– C2

Light switch untidy CPC terminal block – C3

Excess length on otherwise good supplementary bonding – C3

Lack of mechanical protection - C3
 
I’m gonna wade in with what I’d code it as, let the bickering begin.

Pic 1

Missing flashguard for busbar C1(/no intermediate barrier C1) contact with live parts possible
No single means on isolation for CU danger may exist as whole CU is not isolated by main switch the CU would be reasonably assumed to be isolated by a non-competent person i.e installation user and Electric shock risk still exists.C2
Signs of overheating/thermal damage on conductor from cct2 C2
Tails to main switch potentially undersized FI
Cct 8 OCPD oversized for cable csa C2
General comment: connections poorly made on earth and nuetral bars excessive copper showing.

Pic 2

Blanks missing from CU cover C1 contact with l
No OCPD provided for garage sub main C2
Inadequate identification of circuits C3

Pic 3

Thermal damage apparent on nuetral cable FI
Probably cause by loose termination but may be because load is to large for conductor csa or switchgear rating. Circuit isolated with permission from client.

Pic 4&5

Ok it might not be the easiest to tell from the pictures but one of the browns is 1.5mm the one touching the driver.
- CSA of conductor 1.5mm too small for ring circuit without reduction of OCPD C2
(Fitting a FCU remedied this)

Pic 6

Inadequately enclosed conductors C2. Would be C1 if not normally enclosed by the ceiling

Pic 7

Poor terminations in shower switch excessive copper showing. C2
CPC incorrectly identified as nuetral C3

Pic8

Excessive copper showing on nuetral termination. C2
CPC incorrectly terminated twisting is not a sufficient method of connection C2
CPCs not sleeves C2
CPCs not identified C3

Pic 9

Incorrect type of BS951 bonding clamp used for environment. C2
General comment: entry of cabling through the same entry point in the meter housing as gas pipe may not be allowed under gas regulations, recommend that guidance is sought from Registered Gas Safe Engineer.

Pic 10

Not that you knew this but this is actually the top of the CU in pic 1....
- Horizontal top surface of CU not to IP standards (IP4x) ingress if finger possible and potential contact with live parts likely.C1
 
OK, I'll be first to have a go! As some of you know, my experience lies in temporary event power systems (hence the avatar) so please be gentle where I've missed things or misidentified something glaringly obvious to those with the domestic experience I don't have. FWIW I'm planning on tackling 2391-52 next year, so any comments will be helpful.

Busbar internal finger cover missing – C1

Blanking plates missing – C1
CPDs not identified – C3

Evidence of heat damage/burnt loose cable – FI / C1

Modified RFC+spur tails/joint – FI

Omission of sleeving on mixed old & new colours (& check there is a notice at the CU)– C3

Terminal block & earth not continued to lighting fixture (may or may not be required, fixture dependent) – FI / C2

Poor dimmer terminations / incorrect identification of CPC– C2

Light switch untidy CPC terminal block – C3

Excess length on otherwise good supplementary bonding – C3

Lack of mechanical protection - C3
Your on the right track to be fair. There’s a couple of bits and pieces I’d have coded differently. As the inspector with a sound knowledge of the regs you decide what to code it. As long as you can justify it don’t be afraid to code it.
 