As ever LN provides some clues - if only one can spot them! The clue I think I spotted was about the contact only being relevant for the Lister powered genset. Whether it is also relevant to striking and then powering an arc lamp I don't know bit think not because I reckon (no experience of them) arc lamps would have their own control gear to ensure correct current and voltage during striking and running.
If I observed correctly the Gardner engine is started by an electric motor - there are teeth around the flywheel - and as a modern engine for its time would not have relied on an old-fashioned crank handle. What this means is that there is a relatively slow acceleration and ramp up in rotational speed of the engine-generator until the diesel combusts and the rotational speed stabilises.
In contrast the Lister engine has it seems to me a very rapid acceleration from stationary to running speed - an impulse start. What this means is that the magnetic excitation field in the generator rises very quickly and from Faraday's law of induction a very high emf will be induced in the windings. Such high albeit brief excessive over-voltage could cause flash over and damage to insulation within and without the generator. This is not such a problem for the slower rise in speed of the Gardner engine.
What the lower contact does then is connect in a low value high power resistor across the generator during start up to act as a load and prevent an overvoltage. Once running the resistor is switched out of circuit by a trained operator.
Or something like this...

If I observed correctly the Gardner engine is started by an electric motor - there are teeth around the flywheel - and as a modern engine for its time would not have relied on an old-fashioned crank handle. What this means is that there is a relatively slow acceleration and ramp up in rotational speed of the engine-generator until the diesel combusts and the rotational speed stabilises.
In contrast the Lister engine has it seems to me a very rapid acceleration from stationary to running speed - an impulse start. What this means is that the magnetic excitation field in the generator rises very quickly and from Faraday's law of induction a very high emf will be induced in the windings. Such high albeit brief excessive over-voltage could cause flash over and damage to insulation within and without the generator. This is not such a problem for the slower rise in speed of the Gardner engine.
What the lower contact does then is connect in a low value high power resistor across the generator during start up to act as a load and prevent an overvoltage. Once running the resistor is switched out of circuit by a trained operator.
Or something like this...