Today I saw a swa 2.5mm run from a consumer unit to a garage shed about 45m (eyeballed it) from a 16amp breaker....
to a double socket then a fused spur to a led light fixture. Voltage drop would be :
15X16X45/1000
=10.8volts
which complies but I guess its pretty close with power circuits being 5 %, but as it has a light on it shouldn't it have been with in 3%?
to a double socket then a fused spur to a led light fixture. Voltage drop would be :
15X16X45/1000
=10.8volts
which complies but I guess its pretty close with power circuits being 5 %, but as it has a light on it shouldn't it have been with in 3%?
For a lamp holder you couldn't use that justification, but for a permanently wired fitting it could be reasonable. For others, they might not be multi-voltage, but will still provide constant light output over a significant range.