Today I saw a swa 2.5mm run from a consumer unit to a garage shed about 45m (eyeballed it) from a 16amp breaker....

to a double socket then a fused spur to a led light fixture. Voltage drop would be :

15X16X45/1000
=10.8volts

which complies but I guess its pretty close with power circuits being 5 %, but as it has a light on it shouldn't it have been with in 3%?
 
What is the voltage rating of the LED light fitting?
3% is a generic figure applied in the absence of specific data for the lighting installed.
In this situation you can look at the voltage eating of the specific light and establish what the maximum allowable voltage drop for it would be. I expect it will be fine with a 5% drop.
 
In practice the true volt drop will depend on the actual load drawn from the double socket, the light itself will have a negligible effect.
 
Today I saw a swa 2.5mm run from a consumer unit to a garage shed about 45m (eyeballed it) from a 16amp breaker....

to a double socket then a fused spur to a led light fixture. Voltage drop would be :

15X16X45/1000
=10.8volts

which complies but I guess its pretty close with power circuits being 5 %, but as it has a light on it shouldn't it have been with in 3%?
perhaps you should put a voltage regulator
 
Something else to consider ...
Some, but definitely not all, LED fittings (or rather the SMPS inside) are multi-voltage - will run on anything from something like 90V to 260V. For U0 of 240V, that's a heck of a lot of volt drop before it's affected o_O For a lamp holder you couldn't use that justification, but for a permanently wired fitting it could be reasonable. For others, they might not be multi-voltage, but will still provide constant light output over a significant range.
Lets face it, the regs were drawn up in the days when a small change in voltage would make a significant difference to the light put out by an incandescent lamp.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
london
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Voltage drop
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7
Unsolved
--

Advert

Thread statistics

Created
dokkan1080,
Last reply from
Simon47,
Replies
7
Views
2,103

Advert

Back
Top