Here's something I've read, they might be wrong of course.
SO HOW DO WE MEASURE IT?

And Does Metallic Cable Tray Require Bonding? - https://professional-electrician.com/technical/bonding-time/
Yeah i would that’s fair enough as long as you haven’t earthed the tray by ways of fixing exposed conductive parts to it or say fixed the tray to steel which has metallic conduit fixed to it also, this would then earth all metallic parts concerned, so it wouldn’t be easy to test to see if it was extraneous ( which I can’t see how it would be in most circumstances)
 
Like in a factory, say, where you have the bonded main steel structure and take off a bond for any other required...
Egggsackly. free range. ( 3 friggin' words)
 
Last edited:
Yeah i would that’s fair enough as long as you haven’t earthed the tray by ways of fixing exposed conductive parts to it or say fixed the tray to steel which has metallic conduit fixed to it also, this would then earth all metallic parts concerned, so it wouldn’t be easy to test to see if it was extraneous ( which I can’t see how it would be in most circumstances)
And the other one?
 
But what is the use of testing between 2 points if they are connected together somewhere in the installation?
Like for instance a gas pipe and a known earth, but the gas pipe is connected at one end to the boiler which is connected to earth by a cpc. The cpc needs disconnecting at the boiler end then test between earth and the pipe.
That’s just one example you do not necessarily have that scenario every time of having to disconnecting anything.
 
Last edited by a moderator:
Thats the idea of this test; to discover if somehow two points are connected in someway or not.
Extract taken from NAPITS site guide, the point is actually to find out if the metallic conductive part is introducing an earth potential into the installation and by testing between the earth of the installation and the conductive part, that the conductive part under test has a high enough resistance to earth that it doesn’t require bonding to the earthing arrangement of the installation
FA78B2F7-1ECF-472D-A970-6C454CB8E621.jpeg
9320013B-3705-4C2E-B211-39E77FE3E23C.jpeg
It’s
 
Last edited by a moderator:
Extract taken from NAPITS site guide, the point is actually to find out if the metallic conductive part is introducing an earth potential into the installation and by testing between the earth of the installation and the conductive part, that the conductive part under test has a high enough resistance to earth that it doesn’t require bonding to the earthing arrangement of the installation

Fair enough. But that’s just one piece of guidance that says dis the cpc’s, against the two I posted, which suggested using cpc’s as the known earth.

Does Guidance Note 3 or 8 make any suggestions?
 
Fair enough. But that’s just one piece of guidance that says dis the cpc’s, against the two I posted, which suggested using cpc’s as the known earth.

Does Guidance Note 3 or 8 make any suggestions?
It’s only relevant to disconnect the cpc’s if required, you don’t always need to if the metallic part has not been connected together with a cpc to earth .
I don’t think gn3 covers this subject but gn5 and 8 do so I’ll have a dig out
 