P
plancaster
Hi People on an install I have come across a British General outside socket that is reducing the Insulation Resistance when i remove the outside socket the IR goes back up has any one come across this before
Thanks phil
Thanks phil
No never have
As above, if it's an RCD socket then it will give a low reading. A 500v test may cause damage to such a socket. Otherwise if its a standard socket you can always IR the terminals of the disconnected socket to verify.
Thanks phil
Hi it's a brand new socket and non rcd
Phil
What, are the IR readings with, or, without the socket being connected? Does the IR alter if you just slacken the front plate from the back box?
neon should only affect the IR if the socket switch is in the ON position.
Hi its between line and neutral the line conductors and cpc are fine I am not on site but I can not recall it having a neon but could be a poss
phil
Agree Tel but we have nil info on test results or how the tests were carried out.
[automerge]1587745759[/automerge]
phil
As per Tel' response, test with the socket switched off, or removed from yje back box bye still connected, AND GIVE US THE RESULTS OF YOUR TESTS PLEASE.
the reading was between line and neutral read low and the line and earth was fine as for the neon mmm I can not recall if it has one
phil