J
JKMRK1
Question I have is, is it ok to have x2 ring main circuits on one 32amp type B MCB??
If so does this meet the current regs.
TIA.
TIA.
No not really, a circuit originate from 1 OCPD, secondly it's not a "Ring Main" it's a Ring Final Circuit RFC, pedantic but correct terminology counts these days.
Two rings of a circuit, got the regs?
No is the answer, you will overload the mcb
Are you adjusting a circuit or putting another one in and have no room in CU.
Reactions: freddo and pc1966
Yes I have the regs book, which states final circuits should be connected to a seperate way in the CU. But I've seen so many others argue this is OK??
I've never seen many people argue that two ring finals one one MCB is a good idea.
I'll reiterate, a circuit originates from an individual OCPD if some dipstick has decided to combine 2 RFCs into 1 circuit incorrectly then He / She needs to hang up their screwdrivers, and take up another Trade.
I've never seen many people argue that two lring finals one one MCB is a good idea.
the chuckle brothers electrical. Lol
I'm not saying it's correct just saying what I've seen. That's why I've asked the question to make sure its correct.
[automerge]1588089613[/automerge]
Thanks for the advice it is much appreciated?
Well no then it isn't
[automerge]1588089689[/automerge]
You are more than welcome Mate
[automerge]1588089831[/automerge]
See description of a circuit in OSG or BS 7671
You could put more than one radial on a MCB but its not good practice.
2 Rings on 32mcb is dangerous are you sure it's not 2 radials?
2 rings would have four wires goinging into a MCB
Some people spur off a MCB maybe it was that - 3 wires?
If there is a spare way in the CU then I would question why someone has decided to combine the two circuits. I recommend doing full set of dead tests before connecting up.
Definitely two rings there are 4 cables in the MCB. I'm going to add another way and seperate them.
Reactions: Wilko
Looking at this thread there is argument that it is safe but not common
_theiet.org/forums/forum/messageview.cfm?catid=205&threadid=32208
I suppose you could argue it's just extending the Ring??? - 2 large rings would surely cause constant tripping.
it could even be that originally it was 2 circuits.
failed mcb was removed and temporary supply taken from the one next to it.
late night tempory fix that never got finished off?
[/QUOTE]
It's not the same as extending the ring.
I'm not saying I would do this because I wouldn't install like this, but I am going to play devils advocate.
Which regulations does such an arrangement breach?
And how would two ring final circuits installed in accordance with the regulations connected to the same 32A MCB be dangerous?
As I say I wouldn't do it, except as a temporary measure to restore supply, so I'm just curious about the thought process behind the statements.
Unless you have tested it a visual assessment that four conductors equate to two ring final circuits may or may not be correct. It could be four radials, one ring final and two spurs or just all four interconnecting with themselves.
In all honesty I cannot see anything in Bs7671 that this would contravene other than good workmanship. If it originates from one MCB it is a single circuit. Despite what has been said about it overloading there is no reason to assume it would be. A single ring with 10 double sockets could have 20 3kw heaters plugged into it.
Very poor practice though and it needs altering on that basis.
edit. Post crossed with Sparkychick who has reached the same conclusion.
Reactions: Lucien Nunes
Ring main.
JKMRK1,
Risteard,