Question I have is, is it ok to have x2 ring main circuits on one 32amp type B MCB??

If so does this meet the current regs.

TIA.
 

Pete999

-
Esteemed
Arms
Reaction score
16,866
Yes I have the regs book, which states final circuits should be connected to a seperate way in the CU. But I've seen so many others argue this is OK??
I'll reiterate, a circuit originates from an individual OCPD if some dipstick has decided to combine 2 RFCs into 1 circuit incorrectly then He / She needs to hang up their screwdrivers, and take up another Trade.
 
Reaction score
7
I've never seen many people argue that two ring finals one one MCB is a good idea.
I'm not saying it's correct just saying what I've seen. That's why I've asked the question to make sure its correct.
Post automatically merged:

I'll reiterate, a circuit originates from an individual OCPD if some dipstick has decided to combine 2 RFCs into 1 circuit incorrectly then He / She needs to hang up their screwdrivers, and take up another Trade.
Thanks for the advice it is much appreciated👍
 

Pete999

-
Esteemed
Arms
Reaction score
16,866
I'm not saying it's correct just saying what I've seen. That's why I've asked the question to make sure its correct.
Well no then it isn't
Post automatically merged:

I'm not saying it's correct just saying what I've seen. That's why I've asked the question to make sure its correct.
Post automatically merged:


Thanks for the advice it is much appreciated👍
You are more than welcome Mate
Post automatically merged:

I'm not saying it's correct just saying what I've seen. That's why I've asked the question to make sure its correct.
Post automatically merged:


Thanks for the advice it is much appreciated👍
See description of a circuit in OSG or BS 7671
 
Reaction score
83
You could put more than one radial on a MCB but its not good practice.
2 Rings on 32mcb is dangerous are you sure it's not 2 radials?

2 rings would have four wires goinging into a MCB

Some people spur off a MCB maybe it was that - 3 wires?
 