Just seen a you tube video by Artisan, he mentions there is a 15 meter run that goes in the fabric of the building from the meter/100amp cut out to the consumer unit.
it started a debate as to whether to code it a c2 or c3. The question that I have is how would you fix/solve the problem?
the house was a relatively new build as well so how did it pass initial verification?
Discuss.....
 
That’s correct - the tails were unprotected - just run directly from the dno fuse to meter then long run into fuseboard
No there was a switch fuse in a separate cabinet, the issue was that the tails are potentially unprotected in the wall but for all he knows they could be mechanically protected, a limitation in my opinion, you can’t possibly know how they are installed
 
No there was a switch fuse in a separate cabinet, the issue was that the tails are potentially unprotected in the wall but for all he knows they could be mechanically protected, a limitation in my opinion, you can’t possibly know how they are installed
Let’s just assume they are unprotected in the wall for the sake of argument. The question I have is how would you correct the problem?
 
Let’s just assume they are unprotected in the wall for the sake of argument. The question I have is how would you correct the problem?

If the problem is that they are unprotected then the solution must logically be to protect them.

Dig them out and install a heavy gauge metal plate over them would be one soloution, and possibly ideal from an electrical point of view, but not so ideal from the customer point of view.
 
If the tails are in the cavity without being in earthed metal containment , then they would require rcd prot3ction
 
That’s what I thought too but how / where would this be installed. I’ve never had this problem yet Myself but wondered how I would resolve it in the most efficient way.

You can't really as then you'd be putting the whole installation under a single RCD, which is not compliant with section 314.
Another method from 522.6.204 would have to be considered if the cables were less than 50mm deep.
 
Put in the smallest fuse board (4 way?) and take it from/to the db.

If it's feeding the install then have the new enclosure with RCBO (or RCD & MCB) at the servicehead other have it off the main board by a suitable sized RCBO.

I'm probably wrong in my ideas but I'm happy to be properly guided.
 
Unprotected the tails can be Swa,without Rcd protection,otherwise a time delay Rcd @ front.
Then I would supply rcbo’s for outgoing circuits.
 
Time delay RCD won’t comply if it’s for additional protection (which it is).

Your options are protect the cables in the wall with a thick metal plate that can’t be drilled through with sds

or

Replace meter tails with swa
Both options require you to have a switchfuse at the intake position. You can’t rely on DNO’s fuse at that length

Fitting an RCD won’t comply as you risk losing the whole installation in the event of a fault.
 
Time delay RCD won’t comply if it’s for additional protection (which it is).

Your options are protect the cables in the wall with a thick metal plate that can’t be drilled through with sds

or

Replace meter tails with swa
Both options require you to have a switchfuse at the intake position. You can’t rely on DNO’s fuse at that length

Fitting an RCD won’t comply as you risk losing the whole installation in the event of a fault.
There’s a switch fuse at the origin, that’s not the concern
[automerge]1593329691[/automerge]
As the inspector it is impossible to say for certain that the tails are installed incorrectly, cables concealed in the fabric of the building cannot be inspected and are a limitation on the report, as it’s already written for you.
 