This isn't really a useful test but 100V is a perfectly reasonable result for induced voltage. One side of your meter sees earth, the other sees a floating length of CPC that isn't connected to any terminal of the supply. But there is capacitive leakage into it from nearby line conductors, and leakage out of it to nearby neutral conductors and earthy objects, and this forms a potential divider. The actual voltage, often between 1/4 and 1/2 of line voltage, doesn't signify very much other than that there are some live cables around the place.
If you had measured the current from the disconnected CPC to earth, you would probably have found that the leakage is tiny, a fraction of a milliamp.
Thanks for response. .
[automerge]1593714782[/automerge]
Ok. I went and purchased a clamp meter today. For a little test I clamped my main live and neutral 10ma. Out of interest I clamped the main earth. Same reading. 10ma.
So I opened up my board and only cable in that I could easily clamp was my alarm cable. So I clamped live and neutral 130ma approximately. I then clamped the cpc on.its own. 1ma.
Could one of you kind people explain this?
Guessing its electronics in some form.
Also back onto my original large earth leakage issue. How common is it for tncs to be affected with earth leakage from sources external to the property:?
As I say it all points to that conclusion due to the rcds working fine within the installation but just find the issue disconcerting.
Also would you contact dno about it if it's happening or is it acceptable Because I got friend to clamp main earth on a 3 phase large commercial unit today and he was getting similar reading to the house I'm working on.
Sorry for all questions..
The current you are measuring in the earthing conductor is not leakage, it's a fraction of the normal neutral current from any and all installations finding its way through parallel paths connected to the PEN. It's not a problem and it can't be eliminated.
Edward67,
Edward67,