But (most of) the rest of the world does not use fused plugs. Hence the advantage of the ring in terms of high number of sockets and loading diversity from many appliances and a supply MCB well above what would safe for the appliance wiring alone don't really apply.The"radial /ring debate" is one you will only find discussed in the British Isles in my experience. The rest of the world appears to have drawn its own conclusions.
Testing is another long drawn debate as well. The ring final has its own peculiar test strategy as you have both ends to play with (and to verify), but doing so it often a more through test than easily done with a radial set. Also if the radial test is half the time (as Mike suggested) but you have 3 times the number of final circuits you don't gain much!
Both circuits have their places so I don't really get the anti-ring/radial intensity of feelings as usually it comes from not seeing where each is best used.
[automerge]1596482245[/automerge]
Just like investments. Usually down!In reality, the rating factors as Davesparks says may go up or down.
Obvious one that appears from time to time are 16mm tails on a 100A supply fuse - plenty good enough as they are well ventilated and not bunched in a common sheath so getting the heat out is not like most folk remember for 16mm SWA, etc.