Midwest
Following on from the last two more technically debated threads:
32A supply for Hot Tub of a PME supply
Another Hot Tub install
I posted a question, in the last one, but didn't get a reply, so starting another one. Hope the Mods don't mind.
So posting my question again, slightly edited.
I’ve been reading lots of threads, about hot tubs & the like, using a PME supply.
I’m thinking of buying one of those inflatable hot tubs Lazy Spa, primarily as a glorified paddling pool for my grandson. I was quite happy to plug into my outdoor socket on my composite (plastic) decking; I have a PME supply.
But since then, I've been reading all sorts things about extending pme (to an outside environment), and I've been contemplating whether to risk it. Manufacturer recommends connecting to equipotential bonding terminal
My options I know, are to either TT just the supply to the tub socket, use my pme supply and try and supplement that with a rod of <20. My sub soil is littered with rocks. Or just use the pme supply without a rod, and don't worry cause its on my plastic decking.
Or just forget it, and keep filling the paddling pool!
Your thoughts?
In terms of effort, putting a DP RCD or RCBO & basic rod to TT the supply is the simplest and least-effort way for peace of mind.
You only need Ra < 200 ohms and you can probably get that with a short rod or a couple of horizontal buried bare 16mm copper wires 50cm down or whatever is practical and safe enough in that region of your garden. E.g. for wire you get it from places such as:
Unless you have reasonably high water table and long-ish rods I suspect getting Ra < 20 ohms will be a challenge. Or the extra effort for a bigger earth mat style of installation.
The earth mat (or several radial wires) has another attraction, if extending beyond the tub and deep enough down it need not meet 20 ohms for protection as it will still raise the poorly conductive ground above it in that region so [Tub] to [Earth (local)] touch voltage is low enough. But you are looking at a lot of physical effort to do that.
I think the fact you have posted this means you are concerned, and so for peace of mind then a TT arrangement for tub and any outdoor feeding sockets would be of moderate cost and not too much disruption to fit.
no need for any rods. Lazy Spa tubs come with a 10mA RCD built into the lead. it's really just plug and play, whatever earthing system you have.
Thanks. The challenge will be getting an earth rod in, very stony ground. Its too late for an earth mat, as I've had the back garden done.
Of course another alternative might be the ev charger devices. I know there's a little bit of mocking about this, on the you tube sparks, but it is mention at the end of this piece.
I found the LazySpa manual on-line and it says the stuff quoted below.
No mention of supply earthing, but they do have an RCD in the lead, not sure if it in effect TT's the tub. Oddly though they warn about not having a grounded socket!
Also odd they warn against using it in the rain! Buggerall use in Scotland then...
SAFETY INSTRUCTIONS
When installing and using this electrical equipment, basic safety precaution should always be followed, including the following:
READ AND FOLLOW ALL INSTRUCTIONS.
WARNING: RISK OF ELECTRIC SHOCK. Insert the plug only into a properly grounded socket.
WARNING: The spa must be supplied by an isolating transformer or supplied through a residual current device (RCD) having a rated residual operating current not exceeding 30mA.
WARNING: RCD/PRCD must be tested before each use.
WARNING: If the supply cord is damaged, it must be replaced by the manufacturer, its service agent or similarly qualified persons in order to avoid a hazard.
WARNING: To reduce the risk of electric shock, do not use extension cord to connect unit to electric supply; provide a properly located outlet.
WARNING: No part of the appliance is to be located above the bath during use.
WARNING: Parts containing live parts, except parts supplied with safety extra-low voltage not exceeding 12V, must be inaccessible to a person in spa pool; Earthed appliance must be connected to the fixed socket which is permanently connected to fixed wiring. Parts incorporating electrical components, except remote control devices, must be located or fixed so that they cannot fall into the spa pool.
WARNING: The plug of spa shall be more than 3.5m away from the pool.
WARNING: It is necessary to have the plug accessible after installation of the pool.
WARNING: TO AVOID ELECTRIC SHOCK, DO NOT USE THE SPA WHEN IT IS RAINING.
WARNING: This appliance is not intended for use by persons (including children) with reduced physical, sensory or mental capabilities, or lack of experience and knowledge, unless they have been given supervision or instruction concerning use of the appliance by a person responsible for their safety. Children should be supervised to ensure that they do not play with the appliance.
WARNING: To reduce the risk of injury, do not permit children to use this product unless they are closely supervised at all times.
WARNING: Water attracts children; Always attach a spa cover after each use.
WARNING: Do not bury cord. Locate cord to minimize abuse from lawn mowers, hedge trimmers, and other equipment.
WARNING: To reduce the risk of injury, replace damaged cord immediately.
DANGER: Risk of Accidental Drowning. Extreme caution must be exercised to prevent unauthorized access by children. To avoid accidents, ensure that children can not use this spa unless they are supervised at all times.
WARNING: RISK OF INJURY. Never operate spa if the suction fittings are broken or missing. Never replace a suction fitting.
WARNING: RISK OF ELECTRIC SHOCK. Install at least 1.5m from all metal surface.
WARNING: RISK OF ELECTRIC SHOCK. Never operate any electrical appliance when in your spa or when your body is wet. Never place any electric appliance, such as a light, telephone, radio, or television, within 1.5m of spa.
CAUTION: In order to avoid a hazard due to inadvertent resetting of the thermal cut-out, this appliance must not be supplied through an external switching device, such as a timer, or connected to a circuit that is regularly switched on and off by the utility.
WARNING: During pregnancy, soaking in hot water may cause damage to the fetus. Limit use to 10 minutes at a time.
WARNING: TO REDUCE THE RISK OF INJURY:
A. The water in a spa should never exceed 40°C (104°F). Water temperature between 38°C(100°F) and 40°C(104°F) is considered safe for a healthy adult. Lower water temperatures are recommended for young children and when spa use exceeds 10 minutes.
B. Since excessive water temperatures have a high potential for causing fetal damage during the early months of pregnancy, pregnant or possibly pregnant women should limit spa water temperature to 38°C (100°F).
C. Before entering a spa, the user should measure the water temperature with an accurate thermometer since the tolerance of water temperature regulating device varies.
D. The use of alcohol, drugs, or medication before or during spa use may lead to unconsciousness with the possibility of drowning.
E. Obese persons and persons with a history of heart disease, low or high blood pressure, circulatory system problems, or diabetes should consult a physician before using a spa.
F. Persons using medication should consult a physician before using a spa since some medication may induce drowsiness while other medication may affect heart rate, blood pressure, and circulation.
My primary concern, is the loss of pen conductor. The appliance is Class 1, so potentially it could become live through the water heater > water > grandson then stepping onto floor. Long shot I know, but a possibility.
PS, got me links muddle up, I'll post the link for their advice for bonding the pump, when I can get on their web site.
Page 11
Hmmm, cancel my thread. Its now saying the apparatus is Class II :blush:
You sure? Page 11 of that manual has:
Using an extension lead or multi plug adaptor with the spa heater can cause the plug to overheat, causing damage to the equipment and surrounding items. The spa is a class 1 electrical appliance and must be connected directly to a grounded socket. It is recommended to only use a socket which is resistant to humidity and capable of high power loading. Regularly check the plug and socket for signs of damage before using the spa – do not use the spa if the plug or socket is damaged. If you are unsure about the quality of the electrical supply, please consult a qualified electrician before use.
That page also says:
SPA PUMP EQUIPOTENTIAL BONDING TERMINAL
It is recommended to arrange for a qualified electrician to connect the spa pump to an equipotential bonding terminal using a minimum 2.5mm2 solid copper conductor
Where can we find someone like that? <joke alert - in case anyone takes offence>
Yep I posted that before, except I mixed up me links. Also can't see why a Class 2 device would need a PRCD? It does say on their web sites that their tubs are Class 2, but the instructions suggest Class 1.
I've emailed them, they've confirmed my enquiry. I'll post when they come back to me.
i cant belive someone hasnt come up with a contactor that is now allowed to disconnect the L N and cpc of this circuit much the same as the new ev chargers. This would elimate all this confusion.
for my 20pence worth. I use the pme earth unless otherwise stated in manufacturers instructions. If it is required i will isolate cpc (pme)@ the isolator and install a 3/8 rod below the isolator.
I've just watched John Wards vid on ev chargers (June 2020). He's not convinced that those devices will disconnect on all occasions, with a pen disconnect.
I've been trawling around the web, to find a nice looking garage size CU, for my hot tub supply, if I need that. It will have to be located in my down stairs toilet, to keep away from other TN-C-S earths in the house, and close enough for socket location.
Found the FuseBox one, which looked ok. But then came across the Schneider Resti 9 & Easy 9, which you can customize the cover. But Schneider don't seem to do a Type A RCD in those ranges?
It also says not to use their surge protection on TT supplies; my garage unit will be fed from a SPD CU?
One though I had was to use a 4-pole RCD after the usual 2-pole RCD/RCBO to allow the supply to trip including CPC if there was a stray current in the CPC. But that has several issues in practice, such as needing enough volts to trip the RCD and no normal earth currents to confuse it.
Also the PME-derived earth for a hot tub also has the issue that it could be 5-10V above true Earth without any fault which is enough to make a wet person notice it.
I think @bigspark17 suggestion is you break the CPC at the rotary isolator, so your CU has a DP RCD and the SWA out has the PME-derived CPC, but there is a different earth system from the isolator to the tub (and any related sockets).
Of course you need to make sure there is no metalwork, etc, in touchable range that is on a different earth system (e.g railings with a PME-derived earthed floodlight, CCTV camera, etc, mounted on them etc).
Stand alone metalwork in contact with the Earth is fine, as that is your TT rod's system anyway. No harm in bonding to the rod just in case though.
Yep, think I was over engineering things. Don't even need the rotary, just dedicated outdoor socket for the Lay-z-spa. Thanks @bigspark17
Just gotta get an earth rod in somehow. That might prove interesting. Might have to drill a hole, to get through the top layer of stones, below that its clay.
Recently we had to put in some rods through a top layer of tarmac-like stuff on hardcore, with clay below. The hardcore was very hard, chunks of granite which is not typical for here (but is up in Aberdeen, presumably it came from rubble there 70 years ago).
Used an 20mm Armeg SDS drill 1m long to get through the lumpy bits and down far enough the rock could be screwed in to the clay.
Use 2m long M16 stainless threaded rod, angle grinder to cut the tip like a drill, and drove in with the SDS drill adaptor without needing hammer action!
Overkill for your case, but might be something you could look at with a smaller rod, etc.
Would it be desirable to locate the rod away from the likely position of said hot tub?
Still might use a isolator of some sort inside, so supply can be locked off when tub is not in use, to prevent accidental use near other pme fed devices, in the garden.
Main worry with rod location is not to hit buried cables or pipes!
In our case we knew where the local 11kV cable ran and nothing else to worry about :)
Having an indoor DP switch is a good idea generally so you can stop the outdoor socket from being used. I don't see any risk with the socket being used by you for garden equipment, etc, so don't understand the "to prevent accidental use with other pme fed devices" comment.
I would be more worried by local scroats doing something dumb with it...
[automerge]1598194987[/automerge]
If it is just a double socket or so outside then a 20A RCBO and a 20A DP normal wall mount switch are easy options to use. Or even 16A RCBO if cable size an issue, you are unlikely to trip that by overload even with hot tub and a strimmer being used.
Not in the tub, obviously!
The tub we have to do is in a summer house so they can avoid the rain and midges!
watching this thread with interest but I guess I know we’re gonna have to work like bast@&£s to get rods in.
I’ve got other outdoor sockets on pme. I’ve a plan for services, so shouldn’t be hitting anything hopefully.
Yes. Maybe the use of a Rcbo if you have a high integrity cu is ideal but use of an dp rcd would be ok too, yes it could affect or be affected by multiple circuits using same rcd but that is a common problem on dual rcd cu’s. Youre giving rcd protection and isolating pme earth at isolator if required.
Don’t hold your breath, I’ve another project just about to get going. Only thing I’ll do with this one is get the cable in.
Doing my over engineering thing, I’m gonna have two CU’s. Existing one is going to be replaced, and remain in my cinema room, don’t wanna go outside on wet windy nights to the garage to reset things.
I’ll have a small storage area left in the remaining garage, putting another CU in there, as the other one won’t be really accessible to add to. Going for a Wylex CU in the storage are, as they seem to do SP&SwN RCBO’s.
[automerge]1598197263[/automerge]
Might it be an idea to put all of them on TT so you don't have to concern yourself about any class 1 stuff plugged in to extension leads, etc, as well?
I’m comfortable with the use of these sockets. Only used for mainly Class 2 stuff by me.
With regards to Matt:E I (and others) have been pushing them to give an offical line in the sand in the form of a statement on thier website.
Also make sure the Rod is not too close to anything metallic in the ground which would be bonded to the PME MET (gas pipes, etc)
As if you are too close to bonded metal work, the voltage from a PEN fault will appear on the earth rod, and you have situation you are trying to mitigate against
[automerge]1598220309[/automerge]
The single phase Matt:e device is not appropriate to protect a hot tub from PEN conductor faults in my opinion, it gives a false sense of security
It is very possible to have a PEN fault where the voltage between L & N remains within 207v - 253v but the voltage between the PEN and true earth are above 70v, this is due to phase imbalances on the network and also extraneous conductive parts within the installations
[automerge]1598220692[/automerge]
Your thoughts?
Your thoughts?
In the hot weather I looked at how much those Lay-Z-Spas cost, then realised I am short on money from covid plus space to put the thing!
When i was looking into them although, its appeared to me they are class 2 double insulated, I believe the newer models have a heating element sounded in plastic or something like that. So in that case it doesn't matter what the earthing arrangement is as the device doesn't have a connected CPC for any PEN fault voltage to cause a problem.
Think I mentioned that I watch a John Ward video (posted June 2020) that he has his doubts about the likes of the Matt:e charger, for the reasons given by @marcuswareham. in fact he suggested the only real fix is item ii of that reg, being a large earth mat under drive or bond to reinforcing bars in foundations, something @davesparks might like to hear.
I have a new build, so all the services are in plastic, so no metal pipes about. The only other issue is neighbours car chargers. One neighbour has an ev, but he’s gone for a podpoint, which is one of those rod less chargers.
Re the Class 2 issue, Lay-z-spa says Class 2 on their web page spec, but Class 1 in the manuals (it also states the pump should be ‘grounded’, lift from US instructions I suppose). I’ve emailed them for clarification.
I would go for rod(s) that are fairly close to the hot tub location (within safe and practical fixing, of course), after all the goal is not so much "true Earth" as a low voltage difference to anyone stepping in/out of the tub.
Midwest
Oxfordshire
Retired Electrician
Another Hot Tub Thread Part 2
Midwest,
Midwest,