I think @bigspark17 suggestion is you break the CPC at the rotary isolator, so your CU has a DP RCD and the SWA out has the PME-derived CPC, but there is a different earth system from the isolator to the tub (and any related sockets).

Of course you need to make sure there is no metalwork, etc, in touchable range that is on a different earth system (e.g railings with a PME-derived earthed floodlight, CCTV camera, etc, mounted on them etc).

Stand alone metalwork in contact with the Earth is fine, as that is your TT rod's system anyway. No harm in bonding to the rod just in case though.

Yep, think I was over engineering things. Don't even need the rotary, just dedicated outdoor socket for the Lay-z-spa. Thanks @bigspark17

Just gotta get an earth rod in somehow. That might prove interesting. Might have to drill a hole, to get through the top layer of stones, below that its clay.
 
Recently we had to put in some rods through a top layer of tarmac-like stuff on hardcore, with clay below. The hardcore was very hard, chunks of granite which is not typical for here (but is up in Aberdeen, presumably it came from rubble there 70 years ago).

Used an 20mm Armeg SDS drill 1m long to get through the lumpy bits and down far enough the rock could be screwed in to the clay.

Use 2m long M16 stainless threaded rod, angle grinder to cut the tip like a drill, and drove in with the SDS drill adaptor without needing hammer action!

Overkill for your case, but might be something you could look at with a smaller rod, etc.
 
Would it be desirable to locate the rod away from the likely position of said hot tub?

Still might use a isolator of some sort inside, so supply can be locked off when tub is not in use, to prevent accidental use near other pme fed devices, in the garden.
 
Main worry with rod location is not to hit buried cables or pipes!

In our case we knew where the local 11kV cable ran and nothing else to worry about :)

Having an indoor DP switch is a good idea generally so you can stop the outdoor socket from being used. I don't see any risk with the socket being used by you for garden equipment, etc, so don't understand the "to prevent accidental use with other pme fed devices" comment.

I would be more worried by local scroats doing something dumb with it...
[automerge]1598194987[/automerge]
If it is just a double socket or so outside then a 20A RCBO and a 20A DP normal wall mount switch are easy options to use. Or even 16A RCBO if cable size an issue, you are unlikely to trip that by overload even with hot tub and a strimmer being used.

Not in the tub, obviously!
 
The tub we have to do is in a summer house so they can avoid the rain and midges!

watching this thread with interest but I guess I know we’re gonna have to work like bast@&£s to get rods in.
 
Main worry with rod location is not to hit buried cables or pipes!

In our case we knew where the local 11kV cable ran and nothing else to worry about :)

Having an indoor DP switch is a good idea generally so you can stop the outdoor socket from being used. I don't see any risk with the socket being used by you for garden equipment, etc, so don't understand the "to prevent accidental use with other pme fed devices" comment.

I’ve got other outdoor sockets on pme. I’ve a plan for services, so shouldn’t be hitting anything hopefully.
 
Yep, think I was over engineering things. Don't even need the rotary, just dedicated outdoor socket for the Lay-z-spa. Thanks @bigspark17

Just gotta get an earth rod in somehow. That might prove interesting. Might have to drill a hole, to get through the top layer of stones, below that its clay.
Yes. Maybe the use of a Rcbo if you have a high integrity cu is ideal but use of an dp rcd would be ok too, yes it could affect or be affected by multiple circuits using same rcd but that is a common problem on dual rcd cu’s. Youre giving rcd protection and isolating pme earth at isolator if required.
 
The tub we have to do is in a summer house so they can avoid the rain and midges!

watching this thread with interest but I guess I know we’re gonna have to work like bast@&£s to get rods in.
Don’t hold your breath, I’ve another project just about to get going. Only thing I’ll do with this one is get the cable in.
 
Yes. Maybe the use of a Rcbo if you have a high integrity cu is ideal but use of an dp rcd would be ok too, yes it could affect or be affected by multiple circuits using same rcd but that is a common problem on dual rcd cu’s. Youre giving rcd protection and isolating pme earth at isolator if required.
Doing my over engineering thing, I’m gonna have two CU’s. Existing one is going to be replaced, and remain in my cinema room, don’t wanna go outside on wet windy nights to the garage to reset things.

I’ll have a small storage area left in the remaining garage, putting another CU in there, as the other one won’t be really accessible to add to. Going for a Wylex CU in the storage are, as they seem to do SP&SwN RCBO’s.
[automerge]1598197263[/automerge]
Might it be an idea to put all of them on TT so you don't have to concern yourself about any class 1 stuff plugged in to extension leads, etc, as well?
I’m comfortable with the use of these sockets. Only used for mainly Class 2 stuff by me.
 
Might it be an idea to put all of them on TT so you don't have to concern yourself about any class 1 stuff plugged in to extension leads, etc, as well?

you cant stop people plugging in extension leads and throwing them in the bath. You cant stop stupidity im affraid! Dont over think it youll go mad otherwise :/
 
With regards to Matt:E I (and others) have been pushing them to give an offical line in the sand in the form of a statement on thier website.

1598202401274.png
 
I’ve got other outdoor sockets on pme. I’ve a plan for services, so shouldn’t be hitting anything hopefully.
Also make sure the Rod is not too close to anything metallic in the ground which would be bonded to the PME MET (gas pipes, etc)

As if you are too close to bonded metal work, the voltage from a PEN fault will appear on the earth rod, and you have situation you are trying to mitigate against
[automerge]1598220309[/automerge]
With regards to Matt:E I (and others) have been pushing them to give an offical line in the sand in the form of a statement on thier website.

View attachment 60354
The single phase Matt:e device is not appropriate to protect a hot tub from PEN conductor faults in my opinion, it gives a false sense of security

It is very possible to have a PEN fault where the voltage between L & N remains within 207v - 253v but the voltage between the PEN and true earth are above 70v, this is due to phase imbalances on the network and also extraneous conductive parts within the installations
[automerge]1598220692[/automerge]
Following on from the last two more technically debated threads:

32A supply for Hot Tub of a PME supply
Another Hot Tub install

I posted a question, in the last one, but didn't get a reply, so starting another one. Hope the Mods don't mind.

So posting my question again, slightly edited.

I’ve been reading lots of threads, about hot tubs & the like, using a PME supply.

I’m thinking of buying one of those inflatable hot tubs Lazy Spa, primarily as a glorified paddling pool for my grandson. I was quite happy to plug into my outdoor socket on my composite (plastic) decking; I have a PME supply.

But since then, I've been reading all sorts things about extending pme (to an outside environment), and I've been contemplating whether to risk it. Manufacturer recommends connecting to equipotential bonding terminal

My options I know, are to either TT just the supply to the tub socket, use my pme supply and try and supplement that with a rod of <20. My sub soil is littered with rocks. Or just use the pme supply without a rod, and don't worry cause its on my plastic decking.

Or just forget it, and keep filling the paddling pool!

Your thoughts?
Following on from the last two more technically debated threads:

32A supply for Hot Tub of a PME supply
Another Hot Tub install

I posted a question, in the last one, but didn't get a reply, so starting another one. Hope the Mods don't mind.

So posting my question again, slightly edited.

I’ve been reading lots of threads, about hot tubs & the like, using a PME supply.

I’m thinking of buying one of those inflatable hot tubs Lazy Spa, primarily as a glorified paddling pool for my grandson. I was quite happy to plug into my outdoor socket on my composite (plastic) decking; I have a PME supply.

But since then, I've been reading all sorts things about extending pme (to an outside environment), and I've been contemplating whether to risk it. Manufacturer recommends connecting to equipotential bonding terminal

My options I know, are to either TT just the supply to the tub socket, use my pme supply and try and supplement that with a rod of <20. My sub soil is littered with rocks. Or just use the pme supply without a rod, and don't worry cause its on my plastic decking.

Or just forget it, and keep filling the paddling pool!

Your thoughts?
In the hot weather I looked at how much those Lay-Z-Spas cost, then realised I am short on money from covid plus space to put the thing!

When i was looking into them although, its appeared to me they are class 2 double insulated, I believe the newer models have a heating element sounded in plastic or something like that. So in that case it doesn't matter what the earthing arrangement is as the device doesn't have a connected CPC for any PEN fault voltage to cause a problem.
 
Last edited:
Think I mentioned that I watch a John Ward video (posted June 2020) that he has his doubts about the likes of the Matt:e charger, for the reasons given by @marcuswareham. in fact he suggested the only real fix is item ii of that reg, being a large earth mat under drive or bond to reinforcing bars in foundations, something @davesparks might like to hear.

I have a new build, so all the services are in plastic, so no metal pipes about. The only other issue is neighbours car chargers. One neighbour has an ev, but he’s gone for a podpoint, which is one of those rod less chargers.

Re the Class 2 issue, Lay-z-spa says Class 2 on their web page spec, but Class 1 in the manuals (it also states the pump should be ‘grounded’, lift from US instructions I suppose). I’ve emailed them for clarification.
 
I would go for rod(s) that are fairly close to the hot tub location (within safe and practical fixing, of course), after all the goal is not so much "true Earth" as a low voltage difference to anyone stepping in/out of the tub.
 
37 posts discussing how to fi a plug and play hot tub. the mind is flabbergasted, and on reflection, gets flabbered again.
 
37 posts discussing how to fi a plug and play hot tub. the mind is flabbergasted, and on reflection, gets flabbered again.

The manufacturers instructions say to ‘ground’ the pump. I’d rather spend some time getting opinions, before exposing my grandson to any possible dangers. Course I could just not get one.
 

Reply to Another Hot Tub Thread Part 2 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys So I've never installed a hot tub supply before so take it easy on me. I've spent a bit of time researching it myself and its a minefield...
Replies
7
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
535
Hi, My hot tub keeps tripping after 12 years of use. I'm thinking it's the GFCI gone bad. Unfortunately it's a CH 2 pole 50 amp (GFTCB250) and...
Replies
1
Views
886
Hi I am thinking of putting in a Hot Tubat the end of our garden, fed from the a garden shed, more or less next to it, now this might be a silly...
Replies
16
Views
2K
So I have a hot tub to install, in this instance, it is not a problem because there is an existing DB that is TT to provide power for electric car...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock