Are you saying use the pme, and add a local earth rod?Why not use existing way in existing cu to rotary isolator and TT from this location?
Are you saying use the pme, and add a local earth rod?Why not use existing way in existing cu to rotary isolator and TT from this location?
Are you saying use the pme, and add a local earth rod?
no isolate the pme in rotary then continue with the electrode.
I think @bigspark17 suggestion is you break the CPC at the rotary isolator, so your CU has a DP RCD and the SWA out has the PME-derived CPC, but there is a different earth system from the isolator to the tub (and any related sockets).
Of course you need to make sure there is no metalwork, etc, in touchable range that is on a different earth system (e.g railings with a PME-derived earthed floodlight, CCTV camera, etc, mounted on them etc).
Stand alone metalwork in contact with the Earth is fine, as that is your TT rod's system anyway. No harm in bonding to the rod just in case though.

Main worry with rod location is not to hit buried cables or pipes!
In our case we knew where the local 11kV cable ran and nothing else to worry about
Having an indoor DP switch is a good idea generally so you can stop the outdoor socket from being used. I don't see any risk with the socket being used by you for garden equipment, etc, so don't understand the "to prevent accidental use with other pme fed devices" comment.
Yes. Maybe the use of a Rcbo if you have a high integrity cu is ideal but use of an dp rcd would be ok too, yes it could affect or be affected by multiple circuits using same rcd but that is a common problem on dual rcd cu’s. Youre giving rcd protection and isolating pme earth at isolator if required.Yep, think I was over engineering things. Don't even need the rotary, just dedicated outdoor socket for the Lay-z-spa. Thanks @bigspark17
Just gotta get an earth rod in somehow. That might prove interesting. Might have to drill a hole, to get through the top layer of stones, below that its clay.
Don’t hold your breath, I’ve another project just about to get going. Only thing I’ll do with this one is get the cable in.The tub we have to do is in a summer house so they can avoid the rain and midges!
watching this thread with interest but I guess I know we’re gonna have to work like bast@&£s to get rods in.
Might it be an idea to put all of them on TT so you don't have to concern yourself about any class 1 stuff plugged in to extension leads, etc, as well?I’ve got other outdoor sockets on pme.
Doing my over engineering thing, I’m gonna have two CU’s. Existing one is going to be replaced, and remain in my cinema room, don’t wanna go outside on wet windy nights to the garage to reset things.Yes. Maybe the use of a Rcbo if you have a high integrity cu is ideal but use of an dp rcd would be ok too, yes it could affect or be affected by multiple circuits using same rcd but that is a common problem on dual rcd cu’s. Youre giving rcd protection and isolating pme earth at isolator if required.
I’m comfortable with the use of these sockets. Only used for mainly Class 2 stuff by me.Might it be an idea to put all of them on TT so you don't have to concern yourself about any class 1 stuff plugged in to extension leads, etc, as well?