Hello all,

Just got a quick question for you all.

Recently noticed our engineers have been advised to start testing line-loops at every piece of equipment. They are recording the highest and noting this within the comments section on each circuit schedule of test results.

Other than systems conforming to TT and to verify the overcurrent device will operate for any short circuit faults. It seems they are also coding the results based on what results they get.

For example - B63 60898 distribution circuit has a maximum Zs = 0.72 Ohms. If they get higher than this on the line-loop they will also code as C2.

How would I cross reference the results they get?

I was always told if the cable size is adequately sized to the overcurrent device this would be sufficient for any short circuits.

Thanks all.
 
I use the following guide, which I downloaded from the internet. The information is from the 18th edition of regulations.

Circuit breakers and fuses also have a “type” as well as current rating… which is related to their trip time characteristics.

Your example of a 63A 60898 circuit breaker is for a Type 1, not B… which is 0.58 ohms

Comparing the measured readings to this guide has been part of an EICR for years. They should have always been doing this… not just started recently.



IMG_7511.jpeg




IMG_7512.jpeg
 
I think these are old values not taking into account cmin .
IMG_0300.png
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Line-Loop Testing
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
Bradley6969,
Last reply from
newfutile,
Replies
2
Views
92

Advert