If those boards really are without covers / crumbling fuse holders it is not pretty and might explain a C1 code. But from my own (very limited) knowledge of EICR it also comes across as quite contradictory and there are bits that look either wrong or should be commented on, for example:
- First page says satisfactory - then page 2 says not
- 100% coverage and no limitations seems, well, optimistic.
- Primary over-current is given as BS5419, I though it would be ACB but says it is HRC fuses.
- Nature of supply has 'Lim' but above says no limitations?!
- Earthing conductor size not compliant - but given as 300mm
- One circuit (page 6, 3/L1-3) has 6mm cable but 63A fuses, though apparently not in use. Might just be OK for fault clearing.
I kind of lost the will to read on...
As already said, a big job even if it were only upgrading the various DB and identifying what is used and for what.