The earthing is both verified, n/a and unacceptable, although the summary says adequate
[automerge]1602081952[/automerge]
I have been asked to quote remedial based on this.
I think I am leaning to somewhere between 2k and 50k
 
It is totally non specific how can you quote from random comments which aren't quantified.
They have a C2 for earthing conductor size but they have it as 300mm.
 
The earthing is both verified, n/a and unacceptable, although the summary says adequate
[automerge]1602081952[/automerge]
I have been asked to quote remedial based on this.
I think I am leaning to somewhere between 2k and 50k
Not a lot cus I
 
I suggest editing the test schedules and reposting as they contain the site details in the header

I cant edit it now, however if you want to post them a quote based on that (all the info that i have) feel free!
 
Looks like a big job for one. For a start, if it is true that there is no circuit identification you will have to quote for a week maybe, to identify circuits and label etc. That is about £1500. Then (a bit confusing) no cpcs, could mean anything. There does seem to be a Zs for the circuits so hard to know how with no cpc. Can I really believe 300mm earth on 70mm SWA??? I think there are some very mixed up codings on the surface of things. The first or second? item about the distributors earth should not even be on there, that is a matter for the DNO. The 5419 and crumbling insulation seems like a rewire which sound like a massive amount of money considering the size and extent of circuits. You could be working on it until you retire by the sounds of it. And then what about shutting down various parts of the installation work wise for the factory (I guess) so, no idea really. Apart from I think the EICR is very odd in places and contradictory.
 
It isn't a huge site but after looking at it on Google Earth I wouldn't touch it with a barge pole. I have pulled up at many a site like this and sat in the van thinking I will go in in a minute.
 
Don't know that software particularly, but it looks like it might be more designed for domestic with the 'fancy' front page. Wouldn't surprise me if noone looked past the first page in most cases.

I have no experience with industrial or a job of this size, but is it usual to put "not found" on so many circuits? seems like there should be a lot more FI in there.

Also don't like the way that the observations give no help at all as to where the issue is. My software does that - just parrots the reg and then sticks 'needs improvement' on the end, which is no help at all unless you add useful information.

To be honest, seems like to quote at all would need several days on site just working out what any of the observations mean - though looks like many of them might be at the distribution board that's missing a cover, if the pics are to be believed.
 
It is Likely to be a nightmare job, have been to site in the past.
Own transformer in the region of 1 to 1.5Mw
Transformer room has main distribution panel in it and you have to squeeze past the transformer to get to the panel.

I think the eicr is not worth the paper it’s written on, 100% inspection with so many unknown circuits and limitations.

It is a 30 to 50k rewire required, most is in fact 70 years old approximately.

I won’t be taking the job on, it is not the work that I am looking for, I normally repair faults with there machines etc.
 
If those boards really are without covers / crumbling fuse holders it is not pretty and might explain a C1 code. But from my own (very limited) knowledge of EICR it also comes across as quite contradictory and there are bits that look either wrong or should be commented on, for example:
  • First page says satisfactory - then page 2 says not
  • 100% coverage and no limitations seems, well, optimistic.
  • Primary over-current is given as BS5419, I though it would be ACB but says it is HRC fuses.
  • Nature of supply has 'Lim' but above says no limitations?!
  • Earthing conductor size not compliant - but given as 300mm
  • One circuit (page 6, 3/L1-3) has 6mm cable but 63A fuses, though apparently not in use. Might just be OK for fault clearing.
I kind of lost the will to read on...

As already said, a big job even if it were only upgrading the various DB and identifying what is used and for what.
 
If those boards really are without covers / crumbling fuse holders it is not pretty and might explain a C1 code. But from my own (very limited) knowledge of EICR it also comes across as quite contradictory and there are bits that look either wrong or should be commented on, for example:
  • First page says satisfactory - then page 2 says not
  • 100% coverage and no limitations seems, well, optimistic.
  • Primary over-current is given as BS5419, I though it would be ACB but says it is HRC fuses.
  • Nature of supply has 'Lim' but above says no limitations?!
  • Earthing conductor size not compliant - but given as 300mm
  • One circuit (page 6, 3/L1-3) has 6mm cable but 63A fuses, though apparently not in use. Might just be OK for fault clearing.
I kind of lost the will to read on...

As already said, a big job even if it were only upgrading the various DB and identifying what is used and for what.
FYI, the boards pictured hove no internal covers.
They are original and they have a hinged door that is screwed shut.
It was normal for the time they were installed!

I understand loosing the will to read, as you say too much contradiction for my liking.
 