Have you tried testing with the circuit conductors disconnected from the RCBO?RCD test failing on a single outdoor double socket radial circuit (55.8ms on X5). All other tests ok (IR, R1+R2, ZS). Functional test of RCBO ok. Tried circuit on another RCBO and test still fails so not the RCBO.
Am I missing something obvious? Thanks
Yes, it still fails the test with conductors removed. In fact, the issue is with 2 RCBOs on the same board now. Seems odd as they are brand new.Have you tried testing with the circuit conductors disconnected from the RCBO?
Hager Type AWhat make and type of RCBO? A/AC/B???
Thanks for that. The link seems to indicate RCCBs prior to July 2019?Hager recommend testing at the device not at the end of the circuit see this link https://hager.com/uk/support/regulations-18th-edition/updated-rccb-testing
Thanks for that. The link seems to indicate RCCBs prior to July 2019?
I’ve tested at 250ma and 300ma. Still having the same issue. The RCBOs pass the test when MFT is set to AC.are you testing at more than 250 ma we have had hagar rcd’s that don’t meet the required 40ms at 150