Hi all

question regarding the length of surge protector cables. I have read the reg 534.4.8 that states that the length should not exceed 500mm. Is that for each conductor so every conductor should be 500mm or less. So with a 3 phase surge protector all 3 phases/neutral and earth should not exceed 500mm is that correct ? Thanks in advance ?
 
The line(s) conductor and PE in total from the ocpd to the SPD or neutral conductor and PE.
 
Not sure, my thinking is that any of the conductors should not exceed 500mm that’s what I am thinking ?
 
No, I mean that is the answer, the line conductor and PE should ideally not exceed 500 mm and in no cases exceed a meter.
Same applies to the neutral and PE.
 
This could be pretty much impossible to be able to install a SPD on a three phase board external as some consumer units have there earth bars at the top of the boards so defo exceeding 500mm. Could be well over a meter ?
 
This could be pretty much impossible to be able to install a SPD on a three phase board external as some consumer units have there earth bars at the top of the boards so defo exceeding 500mm. Could be well over a meter ?
The Length can be reduced by simply bolting the PE to the earthed chassis of say the DB enclosure, rather than using a separate conductor and adding to the length.
See Hager’s version
 

Attachments

  • 7825CCF8-A633-457D-BD4F-469E88A3E4C7.jpeg
    7825CCF8-A633-457D-BD4F-469E88A3E4C7.jpeg
    788.1 KB · Views: 128
Oh right yeah, they look decent no cable connections either. So to clarify on a three phase consumer unit. It’s the length of the any phase conductor and earth conductor combined that can’t be over 500mm ?
 
Oh right yeah, they look decent no cable connections either. So to clarify on a three phase consumer unit. It’s the length of the any phase conductor and earth conductor combined that can’t be over 500mm ?
Yes pretty much, it can exceed 0.5 meters but not 1meter.
 