I have just carried out an EICR at an old property and found this issue with the main earthing conductor.
It has a TN-S system but the earthing conductor emerging from within the taped up tar coating just before the cut out is only 4mm2 of (what looks like) steel wire armourings. It is 100mm long connected to a small earthing bar. It is not the more popular lead sheathed with earth clamp moulded to it.
My question is, as there is no way to upgrade it without getting involved with DNO cable/equipment, should I just leave the 4mm earth and earthing block close to cut out, then upgrade all earthing from that point on.
Just to point out, at present there is only 4mm earth feeding a BS3036 consumer unit (due for replacement) with 6mm earthing to gas and water. The Ze reading is 0.17 ohms. Adiabatic calculates earth should be 6.19mm2.
Also, what codes for the DNO's undersized earth?
OK big thanks guys. Makes sense to be imperial size due to age. It just looked smaller than standard new 6mm earth but sometimes hard to tell.
So my best bet is to leave alone. Leave earth block in place and just upgrade gas + water bonds and new earth to a new DB from the existing earth block.
Also I forgot to mention in last post (maybe I should start another thread) that the tails from cut out to meter and meter to DB are definitely only 10mm2 fed by 60A BS88 fuse in cut out (there are no seals on the cut out so I could remove easily). This seems very borderline to me. I am surprised a smart meter was fitted 3 years ago with such small tails left in place!
Why change the main bonding?
The landlord has asked me to put right whatever it needs for a satisfactory cert so new DB goes without saying. New earthing from main earth block to DB as its currently less than 6mm. As I've gone this far, it makes sense to upgrade gas and water bonds as they are within same cupboard/area and easily enough to do although I could get away with leaving them as 6mm. Its just for my peace of mind that its done just out of good practice, and the landlord is happy to pay so why wouldn't I upgrade?
I agree with you here I have two rules which I like to stick to. CSA of main earth should be at least half of supply conductors. Also within a TN earthing system should be minimum of 10mm. I do think a 6mm is undersized and needs upgrading just ring the DNO and speak to them I’ve done it many times and sub contracted work from them in my area after speaking to them
Seen loads of these I always make a note on Eicr,Upgrade of Rec MEC required never know if it’s actually done.
doubt if they ever do. that short bare bit of cable will handle fault current for the duration of the fault without melting or setting the house on fire.
Why? (in the general case, acknowledging that there are situations where it is clearly true)
Do you have evidence of bare 7/.044 conductors failing to clear a 100A BS1361? Or does a larger conductor just 'feel' more suitable?
the solder to the lead sheath would melt before that bare bit of 7/.044 overheated.
I give the report to my QS then hopefully he sorts.
So if he failed to act on something you found to be a problem and an injury or fatality was subsequently found to be as a result of something you found would he be the one in court or you
It's the man on the ground that generally cops it as the guy further up the chain covers his back to avoid a stay at one of the HM Hotels around the country
What can you do, you’ve done a EICR,your PDH & QS signs the certification where appropriate,you’ve signed your bit.
You’ve noted the observation you may have coded it, then it’s there duty to do the necessary remedial’s,if required.
As an employee you are then asked to do the works,if those works are not assigned to you,that is not your problem.
How come?
totally agree. yous done your bit. reported findings to the decision makers. it's then up to them to act.
If the means of earthing is still TNS at the cut out then that’s what I use. If the DNO placed PME stickers on the cut out then they would take precedence. But I’ve never seen this without the change to the means of earthing as well. Any new installation I do as if it will be/become PME.
What figures did you use as I did one this past week with a much higher pfc (2.6kA) and k value of 159 (accessible to touch) for bare copper and works out smaller csa than yours.
You may have used the figure for steel but doubt the dno conductor would be steel, its probably tinned copper.
That aside its worthy of a note (C3 at worst), it meets the adiabatic requirements so all good. The consumers installation starts from the MET put in by the DNO so 16sq from that point! Bonding conductors may be terminated from there or the earth bar in the CU.
So if you if you found the DNO earth had failed or the service head was leaking bitumen or crackling am I thinking you would code it and walk away from site and leave your QS to deal with it!!, surely not.
The book stops at the guy who was onsite not the QS if you code something incorrectly or fail to note something it's not your QS that will be talking to the person in the funny wig if something goes wrong.
As an employee ask yourself would your employer back you up or run away and save his own skin should the **** hit the fan, and the only time you will ever find out is when it happens, Take care
You are now asking a different question,which would have a different coding.
Any code 1 would require immediate action.
Regarding my court case,I’ve done nothing wrong.
i would say that if the DNO earth had failed in some way, you might have a load of C1s or C2s as Zs readings could be unacceptable (although bonding could affect these). You are there to report on the installation,nothing more. Once you have passed that report to the higher ups, and maybe left a copy with customer (all depends on you company's policy) you have fulfilled your remit. Being self-employed myself, the responsibility is with me to advise the customer on remedial work (in writing and signed by customer) and it's then the customer's responsibility to act on it. being employed, it's the employer's responsibility to do this, not yours. Also wsoth noting that we do not have the authority to disconnect any dangerous part of an install, unlike gas. all we can do is issue a danger notice if appropriate. end of the day, it's down to the customer to act/not act on the findings of the report.
Pembrokeshire