So why not call the DNO when you are onsite if you have concerns about the earthing arrangementSeen loads of these I always make a note on Eicr,Upgrade of Rec MEC required never know if it’s actually done.
So why not call the DNO when you are onsite if you have concerns about the earthing arrangementSeen loads of these I always make a note on Eicr,Upgrade of Rec MEC required never know if it’s actually done.
I give the report to my QS then hopefully he sorts.So why not call the DNO when you are onsite if you have concerns about the earthing arrangement
we used to call that "passing the buck".I give the report to my QS then hopefully he sorts.
I do think a 6mm is undersized and needs upgrading just ring the DNO
How come?we used to call that "passing the buck".
So if he failed to act on something you found to be a problem and an injury or fatality was subsequently found to be as a result of something you found would he be the one in court or youI give the report to my QS then hopefully he sorts.
What can you do, you’ve done a EICR,your PDH & QS signs the certification where appropriate,you’ve signed your bit.So if he failed to act on something you found to be a problem and an injury or fatality was subsequently found to be as a result of something you found would he be the one in court or you
It's the man on the ground that generally cops it as the guy further up the chain covers his back to avoid a stay at one of the HM Hotels around the country
How come?
totally agree. yous done your bit. reported findings to the decision makers. it's then up to them to act.What can you do, you’ve done a EICR,your PDH & QS signs the certification where appropriate,you’ve signed your bit.
You’ve noted the observation you may have coded it, then it’s there duty to do the necessary remedial’s,if required.
As an employee you are then asked to do the works,if those works are not assigned to you,that is not your problem.
Thank you?totally agree. yous done your bit. reported findings to the decision makers. it's then up to them to act.
Yes. That was my thought. How do you guys confirm its stillIt is a requirement to check the suppliers earthing arrangement.
Agreed. Future proofing way to go.Any new installation I do as if it will be/become PME.
What figures did you use as I did one this past week with a much higher pfc (2.6kA) and k value of 159 (accessible to touch) for bare copper and works out smaller csa than yours.Adiabatic calculates earth should be 6.19mm2.