the solder to the lead sheath would melt before that bare bit of 7/.044 overheated.
 
I give the report to my QS then hopefully he sorts.
So if he failed to act on something you found to be a problem and an injury or fatality was subsequently found to be as a result of something you found would he be the one in court or you

It's the man on the ground that generally cops it as the guy further up the chain covers his back to avoid a stay at one of the HM Hotels around the country
 
So if he failed to act on something you found to be a problem and an injury or fatality was subsequently found to be as a result of something you found would he be the one in court or you

It's the man on the ground that generally cops it as the guy further up the chain covers his back to avoid a stay at one of the HM Hotels around the country
What can you do, you’ve done a EICR,your PDH & QS signs the certification where appropriate,you’ve signed your bit.
You’ve noted the observation you may have coded it, then it’s there duty to do the necessary remedial’s,if required.
As an employee you are then asked to do the works,if those works are not assigned to you,that is not your problem.
 
How come?

What can you do, you’ve done a EICR,your PDH & QS signs the certification where appropriate,you’ve signed your bit.
You’ve noted the observation you may have coded it, then it’s there duty to do the necessary remedial’s,if required.
As an employee you are then asked to do the works,if those works are not assigned to you,that is not your problem.
totally agree. yous done your bit. reported findings to the decision makers. it's then up to them to act.
 
If the means of earthing is still TNS at the cut out then that’s what I use. If the DNO placed PME stickers on the cut out then they would take precedence. But I’ve never seen this without the change to the means of earthing as well. Any new installation I do as if it will be/become PME.
 
Adiabatic calculates earth should be 6.19mm2.
What figures did you use as I did one this past week with a much higher pfc (2.6kA) and k value of 159 (accessible to touch) for bare copper and works out smaller csa than yours.
You may have used the figure for steel but doubt the dno conductor would be steel, its probably tinned copper.

That aside its worthy of a note (C3 at worst), it meets the adiabatic requirements so all good. The consumers installation starts from the MET put in by the DNO so 16sq from that point! Bonding conductors may be terminated from there or the earth bar in the CU.
 