So far, no one has explained to the OP that C3s do not result in an 'unsatisfactory' result. C1s and C2s are the ones that matter.
That appears to be a fair, honest and thorough EICR. There are a number of issues preventing the issuing of a satisfactory report, but most of these could be dealt with by a day's work.
The only thing I disagree with (from here) is the need to replace the CU, but if I was there in person, I might change my mind on that.
@brianmoooore it's ok. I understand about C3 being akin to an advisory on an MOT failure ?
 
The first spark needs to see the work had been done, but the spark doing the the work would need to produce the new test certs which will cost the op again.
@buzzlightyear If reducing my quote from £900 means I have to pay again, then I'm happy to do so. Unless you think that's a fair assessment of the work required? ?
 
For those asking for a pic of the CU, I don't live there at the moment. It's got to be done up and it's a 5-hour round trip ? I'll see if I have any somewhere
 
Photo of CU for those asking.
 

Attachments

  • IMG_20210228_131029.jpg
    IMG_20210228_131029.jpg
    167.6 KB · Views: 82
  • IMG_20210228_130944.jpg
    IMG_20210228_130944.jpg
    154.2 KB · Views: 86
The only think not obvious is the C2 for the IP rating of the CU. Usually that means a hole big enough to get a finger in (e.g. missing blank, but your photo shows that is fine), or smaller one the top where people tend to leave crap that can fall in potentially causing spark/fire.

If it is gaps on the top then it might be that suitable glands could be fitted to seal the unit up. Having said that, if there is going to a an hour or two of work to remove, gland, install and re-test circuits then it might be worth paying the extra £300 or whatever for a new CU at the same time.

Again, more photos showing the top/bottom/side where any holes are would allow folk on here to comment in a more meaningful way.
 