Hello,

An EICR unsatisfactory is claiming all the lights are not fire rated and "do not comply BS7671 too".

Can be classified as C2 if they are not fire rated?
 
Last edited by a moderator:
if it's a house with a single family, (no flat above), and if the ceiling is not a fire barrier, then fire rated are not necessary, altough desirable. C3 at worst.
 
I might code them in a bathroom if within zones as to regards their IP rating, but nothing to do with fire rating.
 
Tell us about the property. Flat or house for a start.
The report should theoretically have enough information for someone else to fix it - does it say how many lights, or where, and how they do not comply with (presumably) BS7671 ?
 
Tell us about the property. Flat or house for a start.
The report should theoretically have enough information for someone else to fix it - does it say how many lights, or where, and how they do not comply with (presumably) BS7671 ?I

Tell us about the property. Flat or house for a start.
The report should theoretically have enough information for someone else to fix it - does it say how many lights, or where, and how they do not comply with (presumably) BS7671 ?
It's an upper flat. The lights are in bathroom(8), kitchen(6), lounge(6), landing(3), bedrooms(4). It doesn't mention why they don't comply, there is only an extra note with "lights have signs of over heating surrounding"
 
Tell us about the property. Flat or house for a start.
The report should theoretically have enough information for someone else to fix it - does it say how many lights, or where, and how they do not comply with (presumably) BS7671 ?
The lights actually tested are 3 in the kitchen, 2 bathroom, 2 hallway, 2 bedroom and 2 lounge
 
Are you saying there are other flats on the same floor, additionally I was asking is there a common loft area, if so the ceiling may be a fire barrier.
 
Hello,

An EICR unsatisfactory is claiming all the lights are not fire rated and "do not comply BS7671 too".

Can be classified as C2 if they are not fire rated?
I would say add rcbo to the lighting circuit, this will provide adequate protection.
 