telectrix

-
Mentor
Arms
basically, done a EICR for rental. 12 way wylex with 3871 MCBs, no RCD at all, so a few C2's and C3's. ideal world is a new CU with RCBOs, or even a dual RCD board. landlord won't pay more than necessary as it's a short term let and due to be demolished as soon as he gets planning for 2 houses on the land. upfront RCD would get rid of the "fails" on the installation, but 1 rogue circuit and the lot is dead. what would you do?
 
Not that.

Either upgrade the consumer unit, as it could well be a long time before the property gets demolished, and the law is the law, and it cannot be let with C2s.

Or maybe (assuming RCBOs for this board are not available) run the circuits that need RCD protection through a separate enclosure with RCBOs in it.
 
be hard enough getting the tight-arse to pay for an upfront RCD in enclosure. mention RCBOs and he has a heart wallet attack. the upfront RCD would get rid of the C2s so would make it safe for use, but non-compliant regarding division of circuits.
 
I hate fitting dual rcd boards but if the property is to be demolished in a few months time I would be inclined to by a second hand rcd board off eBay and fit that as a very temporary fix

you can pick up a dual rcd board for about 30 quid second hand


your customer probably won’t like my Labour charge for doing it , but if it’s an easy swap then you can bill him half a day
 
be hard enough getting the tight-arse to pay for an upfront RCD in enclosure. mention RCBOs and he has a heart wallet attack. the upfront RCD would get rid of the C2s so would make it safe for use, but non-compliant regarding division of circuits.
You asked what we would do.
If the owner is unwilling to pay to comply with a legal requirement, I'm off down the road to the next job...
 
A completely different way of looking at it - One day when he has new houses built (which he claims is soon) he will need a new consumer unit with rcd and probably spd protection to get past building control. No reason I can see that it can't be removed and preserved when demolition occurs.
Granted the labour costs of a board change are higher than an up front rcd but he has to suck that up as he's a landlord and responsible for his tenants safety.
 
if the guy is penny pinching just sling in a cheap screwfix special duo rcd board or buy one off ebay
think that's what he'd go for a 13 way BG dual RCD board. but then he'd want it refitting in 1 of the new houses. not my problem. i'll be out of the game by then (assuming i'm still alive enough to be fed Theakstons by straw).
 
think that's what he'd go for a 13 way BG dual RCD board. but then he'd want it refitting in 1 of the new houses. not my problem. i'll be out of the game by then (assuming i'm still alive enough to be fed Theakstons by straw).
In all seriousness I'd rather fit that £80 delight than nothing at all (once the knock-outs have been removed with dynamite)
 
them rear knockouts are a gem. i finf a 2lb hammer and a sharp cold chisel the easiest.
 
Don't trust any landlord that says it's going to be a short term let, the amount of paperwork and certificates needed to rent out a domestic property now days make short term letting very unprofitable, its so easy for a Landlord to say "Oh there was some planning problems" and two years later they still have not been resolved, don't get suckered in, it's your signature on the EICR.
 
One of my best drunken student party memories , was in a similar situation ,
..I wend out the back door , and wondered what had happened to next door , adjacent properties
part demolished out back , could not tell from front !
Less squatters if house not intact ! Them were the days " squatters rights " .. some aspects of being a landlord have improved , but still a big gamble.
 
Did not know that Lord Lucan was an unqualified electrician, that would explain his disappearing act being so successful. ?
For many years my nearest neighbours were aristocracy and fairly closely related to our current Monarch.
He was high ranking ex military, was never seen outside their house, but could be frequently seen through the kitchen window, slumped over over the table, with a couple of whiskey bottles to hand.
She, on the other hand, was the nicest, most down to earth person you could ever wish to meet, but extremely well spoken, and exuding pure class. No 'nouveau riche' here; this was the real deal.
Was working in their loft on one occasion, when I came across a scrapbook containing illustrated articles and cuttings, mainly from the Daily Telegraph, covering their wedding, her 'coming out' as a debutante, birth announcements, etc.
About a year after Lucan's disappearance, a man moved into the house with them, remained there for many years, and was every bit as reclusive as the Colonel.
 
Last edited:
As an Amazon Associate we earn from qualifying purchases.
Interesting point

In general I prefer separates when it comes to most things electrical and electronic, not just protective devices for a few different reasons

Obviously when you combine an MCB and an RCD , fault finding can become a little more complicated.
Thrown in an AFD on top of that that with occasional random trips

I may be overthinking it
 
Then there's the total cost of the combined device if a section fails like rcd trip times

The whole thing is redundant at ~£300

Most of the reason I prefer separates in general for devices and equipment
 
Last edited:
Interested so I had a look - the photo on eBay is exactly the same as on the CPC/Farnell website (for the part number marked on it) which is just an RCD.
I wouldn't be tempted by the listing! I wonder what you actually get?
CPC price £58 (Inc. vat). Fleabay price £114.
And a lot cheaper again (~£30) if bought from an electrical wholesaler. That's just a bog standard type A RCD.
 
Interested so I had a look - the photo on eBay is exactly the same as on the CPC/Farnell website (for the part number marked on it) which is just an RCD.
I wouldn't be tempted by the listing! I wonder what you actually get?
CPC price £58 (Inc. vat). Fleabay price £114.

The guy selling that simply combs websites for products they think can be sold at a profit. You place an order and they buy from whatever website and have it sent to you - often they use your details to open an account with the site to cover their tracks and avoid being blacklisted. A lot of it is automated by paying a few ££ for software, so the vendor literally sits back and lets the business run itself - at least they do untill goods aren't as advertised or need to be returned for any reason.

Can't explain how they managed to come up with such an inaccurate description for an RCD as images and text are usually lifted straight from another website.
 
Wylex already do combined RCBO/AFDD, DP switching and single width. Price is going to make you squeal though:

Where is @Pretty Mouth when you need a bit of banjo to make folk paddle harder?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

telectrix

Mentor
Arms
-
Joined
Location
cheshire/staffordshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
Telectrix

Thread Information

Title
RCD Quandary.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
60
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
telectrix,
Last reply from
static zap,
Replies
60
Views
5,955

Advert

Back
Top