N
new2this
Ive been asked by a friend to see how what would be required for a classroom of about 25 computers.
Was wondering what size cable and breaker to use, having not done comercial building before any help would be greatly recieved.
Thing you have to remember is its 25 comp bases plus monitors, thats 50 sockets. I said as a guess 10mm cable should be used! Help!
You will have to put this over a number of circuits as if it is a school normally ring main circuits are put on RCD protection where I have come across them.
The reason for this is because with 25 computers the will be a high leakage current to earth thus causing RCD to trip.
Plus you would have difficulty getting 2x10mm into a socket terminal anyway:eek:
Also remember you are likely to have high protective conductor currents so use high integrity earthing or other method to comply with 543.7 BS7671.
As a guide on the RCD's Ive known as few as 10 pieces of IT equipment to take out a 30mA RCD, but newer equipment generally produces less leakage because of improved filters.
Had a similar job about five years ago. Ran tails from panel board to a dedicated cu for the computer room, single pole mccb protecting tails. Three rooms done, three cus. Six ring circuits per room, run in three compartment dado trunking, data run in aswell. Each ring circuit protected by rcbo so problem on one computer does not take out complete classroom. School very happy with result.
you would one hell of a job to put 2 10mm in a socket outlet connection.
as said before spilt the ring over a number of cicuits, will have to be on rcd aswell to conform to 17th regs
would say the same no more than 10 computers on one ringmain.
even if you could get 20mm of cable into a terminal it would create so much pressure on the terminal frame and connector etc i imagine it would fail quickly
i dont know much about IT equipment but wouldnt you want some sort of surge protection and clean earth too?
If you install a cu for the classroom a surge suppressor can be fitted onto the incomer. Nice little units are available now with three flying leads (L,N & E) and are relatively cheap. The requirement for a clean earth is unlikely in a school. The one I worked in is classed as a College of Technology and now has over a dozen computer rooms, direct link with County Council mainframe and feeds to all other schools in the town. There is not a clean earth there.
From my earlier post and what others have said you may be biting off more than you can chew:eek:
Not only that before you can do the job you will have a CRB check because you will be working near children.
Ian, when did he mention working near children?
Adults use classrooms too!;)
Solution
route through tool box for junior hack saw
ahhhh......junior hacksaw
lob off a few strands :eek:
perfect fit :cool:
however unable to fasten socket back due to cable size
route through tool box to find lump hammer
smash each socket back with brute force :eek:
Job well done !! Note to self .. bring along NIC inspector on next visit, this will really get me some browny points. :D
This is not the first time you've mentioned silicone sealant Wayne. Have you bought a job lot of it??????
no i just seen "bodgit and scarper"use it once or twice .never touch the stuff personally.
except for sealing outdoor lights
new2this,
High Tower,