newfutile

~
Arms
I have measured 0.08 to 0.15 ohms between earth and pipework, which according to GN8 makes this extraneous, i guess its bonded inside the flats which i have no access to.

should these be bonded at the communal consumer unit as well?
 

Attachments

  • 735903B5-0E2A-4C93-845A-E522DF05E777.jpeg
    735903B5-0E2A-4C93-845A-E522DF05E777.jpeg
    234.8 KB · Views: 108
Are they single insulated cables feeding that distribution board?
 
Yep the tails are an issue. I’m also instantly suspicious when I see flexible conduit, hopefully not singles inside….
 
No i installed the flexi (on banding) to cross the pipe work , they have twin and earth inside them, the tails are double insulated 19 strand flexi tails.
it’s in a communal cupboard so it needs to be somewhat tenant proof!
 