sythai

~
Arms
Hi Guys

Any advice/ pointers would be appreciated 😉

Have ‘pretty big’ new build house we’re wiring from scratch.

New supply in from DNO is PME, but we have Ze of 0.51 😕

Are DNO obliged to keep this under 0.35?

Wouldn’t be that much of an issue normally if regular size house and meter was attached to house.

Before we came along on the scene Client had separate garage block built, meter permanently sited in here.

We’ve run a SWA sub-main across to house DB 25metres away, but struggling on suitable overcurrent protection. Even at 80amps BS 88…. Max EFLI 0.40!

Don’t really want to be putting new build on TT system, if it comes to it.

Thank you
Sy
 
if disconnection times cannot be achieved by the Breakers then residual current devices can be used.

no need to TT. a PME with a slightly high Ze gives a far better EFLI than any TT could achieve.



although a combination of earth rod and pme may be in order in case of dropped neutrals, but that’s a whole different thread on an abandoned proposed reg change.
 
Listened to a podcast from the E5 group earlier today and DNO guidance states PME ZEs can actually be as high as 0.8. I will try to dig out the pdf
I did hear that a while back.... that they wouldn't be concerned unless above 0.8! But always hoped they wouldn't go by that
 
Have you spoken to the DNO about it.
They might sort it out.
Did raise my concerns with Client before Xmas.... DNO apparently came out straight away (I wasn't on site) said no problem all fine !

Re-checked last week still 0.51😠

I'm going to raise it myself again directly with them, making sure I'm onsite when (if) they re-visit.
 
if disconnection times cannot be achieved by the Breakers then residual current devices can be used.

no need to TT. a PME with a slightly high Ze gives a far better EFLI than any TT could achieve.
Thanks Pete

How does that work with my 80amp sub-main supply though max EFLI is 0.40 for BS-88 ?

My thinking for TT as an option, was if so could then put all on an RCD (time delayed for sub / house db rcbo's) and use 1667 for max ZS values.

Maybe I'm missing something - has been long week!
 