- Reaction score
- 356
Hi Guys
Any advice/ pointers would be appreciated
Have ‘pretty big’ new build house we’re wiring from scratch.
New supply in from DNO is PME, but we have Ze of 0.51
Are DNO obliged to keep this under 0.35?
Wouldn’t be that much of an issue normally if regular size house and meter was attached to house.
Before we came along on the scene Client had separate garage block built, meter permanently sited in here.
We’ve run a SWA sub-main across to house DB 25metres away, but struggling on suitable overcurrent protection. Even at 80amps BS 88…. Max EFLI 0.40!
Don’t really want to be putting new build on TT system, if it comes to it.
Thank you
Sy
Thank you
Sy