Hi Guys

Any advice/ pointers would be appreciated 😉

Have ‘pretty big’ new build house we’re wiring from scratch.

New supply in from DNO is PME, but we have Ze of 0.51 😕

Are DNO obliged to keep this under 0.35?

Wouldn’t be that much of an issue normally if regular size house and meter was attached to house.

Before we came along on the scene Client had separate garage block built, meter permanently sited in here.

We’ve run a SWA sub-main across to house DB 25metres away, but struggling on suitable overcurrent protection. Even at 80amps BS 88…. Max EFLI 0.40!

Don’t really want to be putting new build on TT system, if it comes to it.

Thank you
Sy
 
Are you taking the Ze from source (at the new supply)
 
Listened to a podcast from the E5 group earlier today and DNO guidance states PME ZEs can actually be as high as 0.8. I will try to dig out the pdf
 
  • Like
Reactions: Pretty Mouth
New supply in from DNO is PME, but we have Ze of 0.51
Have you spoken to the DNO about it.
They might sort it out.
 
DNO is not obliged to supply Ze lower than 0.35 ohm; although all DNO strive to achieve it.

It appears to be a common myth!

Edit:

And why on earth (sic) would you consider changing it to TT?
 
Last edited:
Two 60A / 63A sub-mains, to two separate DBs in the house, circuits suitably divided between them! 😆
 
  • Creative
Reactions: sythai
Is it the Zs of the sub main that is high or the Ze in the garage block? What size is the SWA?
 
if disconnection times cannot be achieved by the Breakers then residual current devices can be used.

no need to TT. a PME with a slightly high Ze gives a far better EFLI than any TT could achieve.



although a combination of earth rod and pme may be in order in case of dropped neutrals, but that’s a whole different thread on an abandoned proposed reg change.
 
Listened to a podcast from the E5 group earlier today and DNO guidance states PME ZEs can actually be as high as 0.8. I will try to dig out the pdf
I did hear that a while back.... that they wouldn't be concerned unless above 0.8! But always hoped they wouldn't go by that
 
Have you spoken to the DNO about it.
They might sort it out.
Did raise my concerns with Client before Xmas.... DNO apparently came out straight away (I wasn't on site) said no problem all fine !

Re-checked last week still 0.51😠

I'm going to raise it myself again directly with them, making sure I'm onsite when (if) they re-visit.
 
And why on earth (sic) would you consider changing it to TT?
Open to any other suggestions, any advice would be appreciated 😉.... definitely not my preferred method by far
 
Last edited:
if disconnection times cannot be achieved by the Breakers then residual current devices can be used.

no need to TT. a PME with a slightly high Ze gives a far better EFLI than any TT could achieve.
Thanks Pete

How does that work with my 80amp sub-main supply though max EFLI is 0.40 for BS-88 ?

My thinking for TT as an option, was if so could then put all on an RCD (time delayed for sub / house db rcbo's) and use 1667 for max ZS values.

Maybe I'm missing something - has been long week!
 
  • Like
Reactions: Gurnatronics
100mA S Type RCD on sub main if it comes to it. Then make sure all RCD protection disconnects both line and neutral downstream
 
Thanks Pete

How does that work with my 80amp sub-main supply though max EFLI is 0.40 for BS-88 ?

My thinking for TT as an option, was if so could then put all on an RCD (time delayed for sub / house db rcbo's) and use 1667 for max ZS values.

Maybe I'm missing something - has been long week!
Yes, time delayed rcd on distribution circuits, standard rcd on final circuits - rcds as fault protection.

No need to convert to TT

leave it as TN-C-S and you can still use 0.4s / 5s but add rcd as fault protection where required.

So if the cable from the meter location to cu fails to operate in 5s due to fault, add a time delayed rcd.

If any final circuit fails to operate in 0.4s due to fault add a standard rcd.

If a circuit will operate within these times, then a rcd is not required for fault protection, but may be required for additional protection.
 
You also need to consider the protection for L-N faults which won't be covered by adding RCD's. This often gets missed.

If you have a circuit that has cpc size equal or greater than the neutral and you have inadequate fault current to operate ocpd fast enough with regard to thermal constraints, then you will have same issue with L-N faults. You can add RCD to cover the L-E fault protection, but L-N will not be covered.
 
Last edited:
  • Like
Reactions: WallaceP
You also need to consider the protection for L-N faults which won't be covered by adding RCD's. This often gets missed.
Yes, you still need overcurrent protection for fault protection, and where necessary overload protection, but there is no requirement to achieve the same trip time.

You also have to achieve voltage drop limits etc, etc - basically all the other requirements remain in place.

Using rcd for fault protection is merely a technique to achieve ads
 
You also need to consider the protection for L-N faults which won't be covered by adding RCD's. This often gets missed.
The disconnection times only need to be met for L-E faults, as far as the regs are concerned anyway. Though interestingly there is something in the OSG that leads you to believe they do need to be met for L-N faults. I'll find a page number...
 
  • Like
Reactions: Deleted account

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

sythai

Arms
~
Joined
Location
Devon, United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
High Ze causing headache !
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
62

Advert

Thread statistics

Created
sythai,
Last reply from
sythai,
Replies
62
Views
6,342

Advert