HappyHippyDad
Supporter
I have just put in a sub distribution board in the middle of a field for a new supply for some poly tunnels (soil heating mats and lighting). I have made it a TT.
I have noticed that they have concreted in a number of separate metal hollow poles (see picture) which will be part of the polytunnel. I haven't tested these yet, but they will test as extraneous. If they remain as they are (i.e accessible) do they require Main bonding?
I do get confused with bonding! Every year I re-read up on it, feel I've got it, and then either forget it or a new scenario comes along!
My thoughts are that it will need a 10mm into the nearby DB as it is an 'exposed metallic structural part of the building', which is one of the examples of an extraneous conductive part (411.3.1.2). However, each post is a separate piece of extraneous, so I need to continue this 10mm around the poly tunnel to each post. Is this right? Or, does it not require bonding for whatever reason?
PS.. there will be no livestock in the field at any time.
I can't see why you would. They are outside already so will be at true earth potential and by the look of the photo not a part of the electricsl installation so are just pieces of metal. I could be wrong but if they aren't exposed conductive parts and aren't part of a structure then, i dont see why they would need bonding. Otherwise we will be bonding every random piece of outdoor metal.
I get why you are asking. They pass the 3 point test for being extraneous conductive parts.
I know it sounds odd, but I think I'd loop test them!
I'd want to know whether there is any point/benefit connecting a metal pole in the ground to a metal rod in the ground, and whether it actually lowers the impedance to any degree that is meaningful.
I'm sure everything in there will be RCD protected and you'd need arms like Mr Tickle to touch two of them at once. If it proves that they have reasonable impedance anyway I currently don't see the point of bonding them.
In the event of a faulty rcd that doesn’t disconnect on a TT system in the event of a fault, I think I’d rather as few exposed conductive/extraneous metal parts as possible.
Will there be a floor going in the poly tunnels or will you effectively be standing in the dirt?
I expect they'll be standing on the earth/dirt.
Assuming that they are extraneous and that they will be extended with metallic hoops to for the structure of the polytunnel, I would say that they need to be bonded. You've mentioned a lighting installation, so it might be possible to touch a light fitting and a hoop simultaneously? Also, what about the controls for the heating? Where will they be located and do they have exposed conductive parts?
You may not need a 10mm bonding conductor. Have a look in GN8 as you may be able to use 6mm on your TT system.
Defo if accessories are fixed to the structure it will need MBPC.
Maybe the structure will be linked somehow, & thus only one MBPC point
That's what I was thinking - maybe all the arched poles are joined together by a central pole at the top.
Are these hollow pipes for the metal arches for the tunnel.
I suspect they'll be the hooped plastic pipe type supports... so MDPE water pipe just stuffed into those hollow pipes. The PVC sheeting, when tight, will be part of the structure... until a good gale of wind rips it and it all ends up in the next county !
It might be worth using a 100mA delay incomer, while providing little in the way if direct contact shock protection that way a fault will clear even if a final circuit RCD has failed.