Yes. Would be interesting to know what the total Fli is with all metal legs tied togetherIt would still be fun to loop test them, if only
to have a good laugh if they have lower impedance than the official earth electrode….
Bonding in a home assumes there is little or no hand to foot fault current current flow.We do have to remember that bonding in this case is joining a metal thing in the ground to another metal thing in the ground.
This does, nt apply outside.
Bonding in the home assumes connected metalwork has a low resistance to earth.
This is unlikely to apply in OP, s case.
So what will bonding achieve?. If there is a fault in a class 1 accessory all metalwork becomes live providing multiple fault paths to "real earth".
I think I would prefer unbonded metalwork in this case and ideally use class 2 light fittings /accessories that may be attached to the metalwork