You would get 7.67k ohms with the calculation given. It's just that the calculation we generally use includes taking off 1k ohms for resistance through the body. Hence 22k rather than 23k, or in this case 6.67k rather than 7.67k.
So which of the above figures would be regarded as the cut off point for when something is regarded as extraneous?. There is quite a gap between 7.67 and 22 Kohm.
 
So which of the above figures would be regarded as the cut off point for when something is regarded as extraneous?. There is quite a gap between 7.67 and 22 Kohm.
I'm about to sit down to a cup of earl grey and a few pieces of toblerone to watch a film, so i'm afraid I haven't got the regs to hand. However, this PDF explains it quite well.
I would always class anything below 23K ohms as extraneous.
 

Attachments

Assuming that they are extraneous and that they will be extended with metallic hoops to for the structure of the polytunnel, I would say that they need to be bonded. You've mentioned a lighting installation, so it might be possible to touch a light fitting and a hoop simultaneously? Also, what about the controls for the heating? Where will they be located and do they have exposed conductive parts?

You may not need a 10mm bonding conductor. Have a look in GN8 as you may be able to use 6mm on your TT system.

Your ECA doc gives a clear explanation and I think I would want to bond it if the hoops are metallic (they may well be plastic). It's all about keeping simultaneously accessible bits of metal at the same potential (or no potential at all if they're not extraneous - ie don't bond random metal bits and bobs if they're not extraneous!). The fact it's TT makes no difference and if the RCD fails makes it all the more important.
 
Your ECA doc gives a clear explanation
Won't download for me. What's the doc called?. I can Google it
. It's all about keeping simultaneously accessible bits of metal at the same potential
If simultaneousely accessible and class 1 accessories are used then that changes the scenario significantly. But I understand that previous posts established that the metal posts were not simultaneousely accessible.
 
It's a great document and one of the clearest explanations I've ever seen.
I'm not sure it helps this situation though other than establishing a helpful target let-go current.
See the diagram below and note the bit circled. That wouldn't be there in the situation this thread is discussing.

Isn't the point here that in all cases there's an 1000 ohm path straight to earth with at least 230ma current flowing, whether you add a parallel path through a unbonded pole (roughly 1000+ 110 ohms using value to MET) or a parallel path through an bonded pole (roughly 1000 + 66 ohms)?
Am I thinking about this right or losing marbles?!
1644166027646.png
 
It's a great document and one of the clearest explanations I've ever seen.
I'm not sure it helps this situation though other than establishing a helpful target let-go current.
See the diagram below and note the bit circled. That wouldn't be there in the situation this thread is discussing.

Isn't the point here that in all cases there's an 1000 ohm path straight to earth with at least 230ma current flowing, whether you add a parallel path through a unbonded pole (roughly 1000+ 110 ohms using value to MET) or a parallel path through an bonded pole (roughly 1000 + 66 ohms)?
Am I thinking about this right or losing marbles?!
View attachment 94766
No. Your marbles are very much where they are meant to be. But if I may offer my final comment on this post, it's this. Bonding as a topic is the "gift that keeps on giving" from the point of view that since I, ve been an apprentice no other single electrical subject has caused me more "head scratching" (along with the occasional headache.) The electrical game would be very boring without it🙂
 
By standing on the soil you'd probably be wearing shoes that provide some level of insulation. Touching a metal pole with bare skin will give a lower impedance to earth. Also it would be a case of resistors in parallel so the two paths combined would give a reduced total impedance to earth.
 
Hi guys,

Similar situation here, except, the aluminium tunnel support hoops are bolted to a new concrete pad.

I havent started yet, but would the hoops need bonding?

The only thing that is going in is a small db, and two double sockets on a ply board mounted on a bespoke metal tube frame at one end.
 