You would get 7.67k ohms with the calculation given. It's just that the calculation we generally use includes taking off 1k ohms for resistance through the body. Hence 22k rather than 23k, or in this case 6.67k rather than 7.67k.
So which of the above figures would be regarded as the cut off point for when something is regarded as extraneous?. There is quite a gap between 7.67 and 22 Kohm.
 
So which of the above figures would be regarded as the cut off point for when something is regarded as extraneous?. There is quite a gap between 7.67 and 22 Kohm.
I'm about to sit down to a cup of earl grey and a few pieces of toblerone to watch a film, so i'm afraid I haven't got the regs to hand. However, this PDF explains it quite well.
I would always class anything below 23K ohms as extraneous.
 

Attachments

  • Extraneous-conductive-parts-17_edition_factsheet_05.pdf
    103.4 KB · Views: 18
Assuming that they are extraneous and that they will be extended with metallic hoops to for the structure of the polytunnel, I would say that they need to be bonded. You've mentioned a lighting installation, so it might be possible to touch a light fitting and a hoop simultaneously? Also, what about the controls for the heating? Where will they be located and do they have exposed conductive parts?

You may not need a 10mm bonding conductor. Have a look in GN8 as you may be able to use 6mm on your TT system.

Your ECA doc gives a clear explanation and I think I would want to bond it if the hoops are metallic (they may well be plastic). It's all about keeping simultaneously accessible bits of metal at the same potential (or no potential at all if they're not extraneous - ie don't bond random metal bits and bobs if they're not extraneous!). The fact it's TT makes no difference and if the RCD fails makes it all the more important.
 
Your ECA doc gives a clear explanation
Won't download for me. What's the doc called?. I can Google it
. It's all about keeping simultaneously accessible bits of metal at the same potential
If simultaneousely accessible and class 1 accessories are used then that changes the scenario significantly. But I understand that previous posts established that the metal posts were not simultaneousely accessible.
 
It's a great document and one of the clearest explanations I've ever seen.
I'm not sure it helps this situation though other than establishing a helpful target let-go current.
See the diagram below and note the bit circled. That wouldn't be there in the situation this thread is discussing.

Isn't the point here that in all cases there's an 1000 ohm path straight to earth with at least 230ma current flowing, whether you add a parallel path through a unbonded pole (roughly 1000+ 110 ohms using value to MET) or a parallel path through an bonded pole (roughly 1000 + 66 ohms)?
Am I thinking about this right or losing marbles?!
1644166027646.png
 

Reply to Does this need to be bonded? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

No waffling, going to get straight to the point. Main water on the exterior of the building in plastic. Changes to copper inside the building...
Replies
24
Views
851
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
709
Hi all, I would like some advice on a scenario currently at my workplace. I am replacing a Sub main DB and replacing the wiring to sockets/lights...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock