I just want to check how I should be interpreting section 705.

705.411.1 states required disconnection devices, the first two indents covering final circuits and sockets, requiring 30ma and 100ma RCD's depending on rating of socket.
Indent 3 says " all other circuits" need 300ma RCD.

Does that include distribution circuits, outside? Or is the word "final" implied?

The background - a fused down main supply circuit runs along the drive of an estate. About half way along the drive there is a main distribution cabinet. This used to be the drive side of the fence but has been moved to other side of fence, field of (usually) sheep.

It's in a massive IP rated double door enclosure. Several distribution circuits leave here going underground, with about 1 ft of SWA being accessible from ground to bottom of enclosure.

2 new circuits run to new hook up points within the same field. (This has created multiple issues with isolators and wiring systems being accessible to animals, and these will need to be resolved)

But the main question is whether an distribution circuit with the source and destination within a field with livestock needs to comply with 705.411.1 iii)
A secondary question is whether an underground distribution circuit with the source in a field with livestock and the destination elsewhere e.g. a house needs to comply with 705.411.1 iii)

It feels as though the intent of that reg is fire protection and aimed at indoor circuits but the wording is actually quite vague.
Getting the cabinet fenced off (carefully missing cables!) is of course an option.
 
TL;DR
Do outdoor distribution circuits in a section 705 location require 300m RCD protection?
Whats the earthing arrangement.

Mainly TNCS.
One set of hook-up points is definitely TT'd.
I'd need to check the other but I believe it is much higher and connected to supplier earth.

I'd also comment that Section 705 didn't say quite what I thought it said about that.
It says it shall not be TNC (combined and never separated again) with a note underneath saying that it doesn't preclude the use of TNCS. (TNC is banned in the UK anyway making that bit somewhat of a red herring)

I'd also comment that we are talking about 2 fields here, no farm buildings containing livestock at all.
The more I look at this place the more complex it gets. A diagram is forthcoming....
 
It's certainly very confusing, reading through it, my take is this distribution circuit needs at least 300 Ma RCD protection, due to the location. Also it will give selectivity and discrimination for RCD protection used at the other end of the circuit/ circuits. What's your opinion Tim
 
Last edited:
Thanks for looking through it.
My take is that it's a circuit in a location covered by 705 and needs RCD protection.
I still believe the intent of the reg is fire protection in buildings, not distro circuits buried underground.

This distribution box is a massive Hager board with x160 moulded case circuit breakers. It would have cost a fortune.
Not enough thought went into moving it to it's current location.
 
705.411.1 states required disconnection devices, the
Indent 3 says " all other circuits" need 300ma RCD.
(iii) In all other circuits, RCDs with a rated residual operating current not exceeding 300 mA.

Is this just a distribution cabinet with no outlets


705.513.2 Accessibility by livestock
Electrical equipment generally shall be inaccessible to livestock.
 
Last edited:
Is this just a distribution cabinet with no outlets
Yes.
Quick sketch:
1722200740971.png
Distro cabinet D has no outlets, it's a metal distribution panel within an IP rated box mounted within a timber 'bus shelter' style structure.
Enduring question is whether D being inside the field mean outgoing distribution circuits need 300ma RCD protection.

Other concerns exist about Sockets A being low and accessible to animals. They are at least all RCD protected and TT'd.
Rotary Isolators are also accessible to animals which is specifically mentioned in another reg.
So there are definite issues there.

Sockets B are much higher up, well out of reach of sheep, but are 2 x 32A sockets and 1 x 63 amp, and they are all 300ma integral RCDs, so that is another problem.
705.513.2 Accessibility by livestock
Electrical equipment generally shall be inaccessible to livestock.
I believe the panel within an IP rated cabinet is sufficient protection.

The pragmatic side of me says that if the cable is deep enough, the only difference between it being there and not being there are the short sections between ground and panel, and if they were adequately mechanically protected then I can't see any benefit to RCD protecting it. As I've said before, I think fire protection inside a building is the intent of the reg.
 
Sheep won't hurt anything. Cattle won't bite anything, but they'll lick and pull with their rasp like tongues. Horses are the ones you need to worry about.
Reminded me of the SWA I left in an open trench overnight. Horse found it. Pity it wasn't energised.
...and that is the thing. I don't think the RCD bit is actually a problem in the real world at all.

I want a C3.5 - "Improvement NOT Recommended but I've noticed it"
 
Section 705 does not differentiate between final circuits a distribution circuits so in my opinion 300ma RCD protection is required.
As you say 300ma is often used for protection against the risk of fire, see Regulation 532.2 and 705.422.7.
I agree that this must be an extremely low risk in terms of a fire hazard but I'm not sure how you can interpret it any different.
 
For what it's worth I agree with Westward.

Hence - all circuits, whether final or distribution, must be protected by 300mA RCD at the top of the tree. Then final circuits that feed socket outlets need either 100mA or 30mA, depending on the rating of the socket outlets. This applies whether the location is indoors or outdoors, according to the scope at the beginning of section 705.

It may also apply to other locations that are in common buildings, for example - the cable that feeds the location may also need to be protected by a 300mA RCD.

As to the reason for the 300mA RCD being required, it is not for fire protection, as this is dealt with as a separate requirement in 705.422.7
 
Thanks @loz2754.

Out of academic interest, you are right about the reason. Having just read the 16th edition equivalent section it's basically the result of simplifying many very complicated regs about EEBADS, protection from indirect contact to exposed conductive parts, and requiring reduced disconnection times. (Interestingly distribution circuits were in fact excepted back then).
Requiring absolutely everything to be RCD protected in this context makes a little more sense.
--

The thing now occupying my brain is "what if D was fenced off".
The supply circuit and circuits to house and camp site become out of scope.
But the distribution circuits going into the field serving points in the field still need 300ma RCD protection.

In some ways sticking a 300ma RCD at source of it all would put this issue to bed, but would also mess up loop testing for evermore for lots of things! I'm there again tomorrow and will have a think.
 
Yes.
Quick sketch:
View attachment 117323
Distro cabinet D has no outlets, it's a metal distribution panel within an IP rated box mounted within a timber 'bus shelter' style structure.
Enduring question is whether D being inside the field mean outgoing distribution circuits need 300ma RCD protection.

Other concerns exist about Sockets A being low and accessible to animals. They are at least all RCD protected and TT'd.
Rotary Isolators are also accessible to animals which is specifically mentioned in another reg.
So there are definite issues there.

Sockets B are much higher up, well out of reach of sheep, but are 2 x 32A sockets and 1 x 63 amp, and they are all 300ma integral RCDs, so that is another problem.

I believe the panel within an IP rated cabinet is sufficient protection.

The pragmatic side of me says that if the cable is deep enough, the only difference between it being there and not being there are the short sections between ground and panel, and if they were adequately mechanically protected then I can't see any benefit to RCD protecting it. As I've said before, I think fire protection inside a building is the intent of the reg.
Is the Tncs taken to the cabinet and divorced from there or is the Tncs taken to the other dbs and TT from there.
 
Last edited:
Is the Tncs taken to the cabinet and divorced from there or is the Tncs taken to the other dbs and TT from there.
SWA is TNCS, isolated at point of entry to other cabinets, then TT.
So no requirement for RCD for fault protection of cable if that is what you were getting at!
 
SWA is TNCS, isolated at point of entry to other cabinets, then TT.
So no requirement for RCD for fault protection of cable if that is what you were getting at!
And in any case, 705.411.1 requires RCDs for all circuits "whatever the type of earthing system".
 
And in any case, 705.411.1 requires RCDs for all circuits "whatever the type of earthing system".
I don’t believe 705 would apply to a distribution cabinet that has no extraneous, no outlets and is inaccessible to animals
 
I don’t believe 705 would apply to a distribution cabinet that has no extraneous, no outlets and is inaccessible to animals
I'll take some photo's tomorrow or maybe tonight as I've been dragged there for other reasons.

If we decide the cabinet is 'inaccessible' to animals, and the cables underground are, well, underground, it remains the case that there are distribution circuits supplying points in the field that are not RCD protected.
 
Ok photos.
The distro box D
IMG_6131.jpeg

The more concerning hook up point (the mobile units go before the sheep arrive)

IMG_6132.jpeg
 
Last edited:
1. The requirements for protection against electric shock apply to agricultural or horticultural premises, indoor or outdoor, irrespective of the presence or otherwise of livestock.

2. A distribution cabinet/enclosure is itself included in the definition of electrical equipment, and if it is accessible to livestock, further measures need to be introduced to prevent the livestock interfering with the equipment. (Build a fence around it for example).
 
1. The requirements for protection against electric shock apply to agricultural or horticultural premises, indoor or outdoor, irrespective of the presence or otherwise of livestock.
In locations intended for livestock,

If there is no intention of having livestock, then I'm pretty sure the risk is quite low.
 
Let's not get into a debate about whether 705 applies, for me that is without question as for at least 4 months of a year there are sheep in that there field!

Here is where I am at:

That locked cabinet is the outer cabinet. Inside is a further metal distribution panel with a locked door. It could easily have a fence around it. A fence around it could take it completely out of the special location.

If a lockable front and back panel was made for the hookup points, we then have a distribution box outside the special location, a reasonably sheep-proof box, and every outlet 30ma RCD protected.

Given the history of the reg and taking into consideration the use of the field and the livestock concerned, I'm not considering that it's a C2 that the inaccessible underground cable between the two doesn't have RCD protection. I've asked how deep it was laid and been told 1.2m.
I'll sleep on it but at the moment it's going to be a C3.

If anyone thinks I'm underplaying any risks then let's talk about it; I do very much value the collective wisdom of you lot!
 
If it were me would fit a 300ma RCD at source. Then at the end of the day you have met the requirements of 705.
So far every C3 I've issued has been actioned, so it could well still happen.
I'm intending to C2 the livestock access to distribution panel /cables and access to hookups as I consider them more potentially dangerous.
But before deciding on the remedy I need to declare how dangerous a cable 1.2m underneath some sheep without RCD protection is. I'm open to my opinion being swayed by reasoning.
To provoke thinking - if it turned out (as I have no idea) that the supply to the house ran under the same field, would that be potentially dangerous?
 
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the hook up points.
In another life, I have shorn sheep, played midwife to sheep, de-tailed (and other things) sheep, performed chiropodist services on sheep, fed sheep and housed sheep. Hundreds of them. I know how sheep behave, and the only thing they'd do to those cables on the ground is to trample them.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

timhoward

Broke Internet
Esteemed
Arms
Supporter
-
Joined
Location
Oswestry

Thread Information

Title
Distribution circuits in Section 705 location, RCD needed?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
29

Advert

Thread statistics

Created
timhoward,
Last reply from
brianmoooore,
Replies
29
Views
2,461

Advert

Back
Top