December 2011.
Section A.
1) Yes, yes, yes.
2) (a) Yes, also ESQR 2002. (b) Yes.
3) (a) No. Remember to read the question. Look at an EIC/EICR model form. The supply parameters are Nominal voltage, Nominal frequency, PFC and Ze.
The only ones that cannot be measured are the nominal voltage and frequency.
(b) as above, PFC and Ze.
4) No. The purpouse is the determine that the installation complies with BS7671 and has been constructed as per the design.
5) Yes.
6) (a) Yes. (b) No. EFLI tester. (c) Yes.
7) Yes, yes, yes.
8) Yes, yes, yes.