Refurbishment of dwelling has taken place and the clients insurance company requires a periodic inspection and test to be carried out, A new circuit supplying 9kw electric shower has been installed, No previous records for the installation are available.

What information does the inspector require from insurance company?

Questions 1

A- the minimum sample size of the initial verification
B- the maximum sample size of the initial verification
C- the minimum sample size of the inspection
D-the maximum sample size of the periodic inspection

Question 2

Where would the inspector record the requirements for the insurance company?

A- limitations section of the electrical installation certificate
B- Declaration section on the electrical installation report.
C- limitations section of the electrical installation condition report
D- Declaration section on the electrical installation condition report


Question 4

What, according to GN3, is suggested minimum sample size for inspection of the existing circuits?

A- 10%
B- 20%
C- 30%
D- 50%
 
Last edited by a moderator:
I would suggest you reply stating what you would answer and why for each of those questions.

We're not here to do your work and sit your exams/mock exams for you, but we will offer advice about answers and the thinking behind them.

And for question 4... if you've not already got guidance note 3, might be a good plan to buy a copy and have a read.
 
  • Like
Reactions: DPG
Upvote 0
Has chicken hen says, come back with answers we will check it.
 
  • Like
Reactions: DPG
Upvote 0
Has chicken hen says, come back with answers we will check it.

On Question number1 I answered D

On question number2 I answered C

On questions number I answered A


I just want to make sure I got it write I have all three books but these questions doing my head in tbh
 
Upvote 0
It is asking for a periodic inspection so one answer in Q1 can be eliminated, two answers in Q2 can be eliminated.
Answers B and D in Q1 are exactly the same?
 
Upvote 0
It is asking for a periodic inspection so one answer in Q1 can be eliminated, two answers in Q2 can be eliminated.
Answers B and D in Q1 are exactly the same?
Sorry my mistake B should be the maximum simple size for the initial verification
 
Upvote 0
Sorry my mistake B should be the maximum simple size for the initial verification
Okay in have edited that meaning two answers in Q1 can be eliminated.
 
Upvote 0
So to Q1, two answers can be ignored. What is the insurance company likely to want, a minimum or a maximum.
 
Upvote 0
So to Q1, two answers can be ignored. What is the insurance company likely to want, a minimum or a maximum.
I would say maximum because its s new circuit and must be checked 100%
 
Upvote 0
So does the inspection and test only cover the new circuit?
 
Upvote 0
Ye
So does the inspection and test only cover the new circuit?
Yes it doest because its part of the system and EIC should be issued
 
Upvote 0
It says a dwelling has been refurbished and they require a periodic inspection. To me this suggests a test of the whole installation and the fact a new circuit for the shower has been installed is just information.
 
Upvote 0
It says a dwelling has been refurbished and they require a periodic inspection. To me this suggests a test of the whole installation and the fact a new circuit for the shower has been installed is just information.
Yes you are right but the way city and guilds put these questions I did really confuse me

I would kindly appreciate if you could answer these questions the rest of the questions I know them very well
 
Upvote 0
It says a dwelling has been refurbished and they require a periodic inspection. To me this suggests a test of the whole installation and the fact a new circuit for the shower has been installed is just information.
But if you look at the other questions it's in the same sennorio it's asking about the sample size do I would say its an EICR
 
Upvote 0
Q1 boils down to answers C and D so minimum or maximum.
Minimum sets a target, if I said to you the minimum I want you to do is cut the grass and weed my flower beds then this is the target but if you choose you can do more. Maximum does not set a target it just indicates you don't need to hit it at all. Again the maximum I want you to do is cut my grass and weed the flower beds but this does not indicate you must do both.
Which one would they chose?
 
Upvote 0
Q1 boils down to answers C and D so minimum or maximum.
Minimum sets a target, if I said to you the minimum I want you to do is cut the grass and weed my flower beds then this is the target but if you choose you can do more. Maximum does not set a target it just indicates you don't need to hit it at all. Again the maximum I want you to do is cut my grass and weed the flower beds but this does not indicate you must do both.
Which one would they chose?
I put maximum sample size for the periodic inspection
 
Upvote 0
You are not seeing the difference. Minimum is the base of what you must achieve, maximum is the upper limit it does not set a base target.
The minimum number of circuits to test is ten, this means test ten.
The maximum numbed of circuits to test is ten, this does not mean test ten.
 
Last edited:
  • Like
Reactions: sameer
Upvote 0
You are not seeing the difference. Minimum is the base of what you must achieve, maximum is the upper limit it does not set a base target.
The minimum number of circuits to test is ten, this means test ten.
The maximum numbed of circuits to test is ten, this does mean

So the correct answer is minimum sample for inspection then
 
  • Agree
Reactions: westward10
Upvote 0
Check out pages 92 and 93 of GN3 for help.
 
Upvote 0

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Wolverhampton
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
2391-52 exam questions need help.
Prefix
N/A
Forum
Electrician Courses : Electrical Quals
Start date
Last reply date
Replies
18
Unsolved
--

Advert

Thread statistics

Created
sameer,
Last reply from
richy3333,
Replies
18
Views
3,363

Advert

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.