bottom of page 24........ pme not recommended unless a metal grid is in the floor! ffs I think I'm going to price to TT the bitch and be done with it.
Can you chaps just answer me the question of whether I still need to meet my 0.2 sec discon times for the 32A tp panels? as its not in section 705 - just says rcd ratings.
installing 30mA protection on each one would at least reduce the likelihood of the incoming type S tripping - if ever, as it stands now a decent fault on any of the pumps has the ability to trip the entire site.
ps thanks everybody for their input, including the hijacker! all aids the cause