Dartlec
Arms
i agree with you, ref: post 10
just wondered if you could help me back it up with something easy to quote!
Maybe:
132.12
Accessibility of electrical equipment Electrical equipment shall be arranged to provide:
(i) sufficient space for the initial installation and later replacement of individual items of electrical equipment
(ii) accessibility for operation, inspection, testing, fault detection, maintenance and repair
Though as usual thats open to interpretation.
If it is domestic:
421.1.201 Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall:
(i) have their enclosure manufactured from non-combustible material, or
(ii) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation 132.12
Which would suggest that the lid being closed isn't necessary for part (i) - though perhaps there is something in 61439-3 re lids?
I'd bet that the manufacturers of the consumer unit themselves don't specify that it can be installed as it is, if only because they didn't expect anyone to do so.