Hi all,

So I’ve been having a strange fault in my house which has just appeared over the past few days. About a month ago I moved my pc set up into the sun house to make space for my second kid.

Inside the sun house/garage I have a DB that is fed of a 40A type B breaker fed by a 6mm core cable.( it’s not a SWA it’s a wierd cable with loads of little cables as a neutral) but I have insulation resistance tested that feed cable and it’s all good. On the garage DB I have a 32A ring main and a 6a lighting circuit. I have had my pc setup in there for a few weeks now and it’s been totally fine up until a few days ago when the 40A MCB is tripping of at random times. It can go off when I’m there and gaming or off through the day when I’m at work.

The circuits in the garage have all tested out totally fine and the feed cable going to the garage DB has tested out fine as well. But for some reason the 40A MCB in my board keeps tripping off. I have changed the MCB as of yesterday and it has went off again today whilst I was at work. There is nothing on in the sun house when the MCB trips. 40A is huge MCB for a house and I can’t get my head round what is causing it because there isn’t even anything above 10A going through that circuit.

Now this would be fine if it was just this circuit going off. As I could slowly work my way through what is wrong with it. But over the past 4 days as well as my garage MCB tripping I’ve had both upstairs and downstairs rings trip off, and as of today the upstairs lights have also tripped off.

They sometimes trip at the same time as the garage but they have tripped off just by themselves. I have tested all the rings and they appear to have no issues with the cables.

What makes it even more confusing is I have a split RCD DB, not once has the RCDs ever tripped on either side. But I have had the garage MCB trip on the left RCD and lights on the right RCD trip at the same time. This has also happened with the ring mains in the house.

I can’t get my head around how a single circuit on its own like the garage can appear to have an effect on another single circuit that are on separate RCDs.

Could it be an issue with the DB itself? Because as far as I can tell after testing each cable they haven’t got any issues. The MCBs can stay on for hours and just trip off.

Any help into this would be great as I’ve been pulling my hair out for days now.

Thanks, Lewis
 
Lewis Curle: have you been able to investigate this problem further to your last message?
Long time no speak everyone, so after a busy few months with the new baby I’m back to trying to figure this fault out. I’ve not been standing idle, I have tried multiple things to try and figure out this bizarre issue.

Short story of it all is I have changed the whole consumer unit in my house for a brand new Wylex one. It’s a split RCD board. First thing I did after changing it was of course test the thing. The issue is still exactly the same after about half an hour of being in the sun house gaming away the sun house MCB tripped along with the upstairs ring and the smoke alarms. Smoke alarms have never tripped before but the upstairs ring has. This was the only time since the new board that those other MCBs have tripped.

So naturally I started to break down the sun house in stages again, I disconnected everything out of the garage DB and the MCB still tripped sometime when I was at work the next day. So i then disconnected the cable feeding that garage DB and taped the ends up and put them safely out of the way of anything. The MCB still tripped. So then I disconnected the the cable at the house db end. And some how the 40A MCB with nothing in it has tripped three times in the past three days. So the sun house has nothing to do with this strange fault in my eyes.

Now I can’t workout how that MCB is still tripping with nothing connected into the thing. The only thing that hasn’t been changed now is the cable that is feeding my DB from the meter box. Nothing has showed up on testing that cable, it has been properly tested and all the results came back perfectly. So now I don’t really have a clue on what to try, other than changing that cable which would be a nightmare to change.

As an electrician I can’t make any sense of it.

I’ve has the grid people out and they have checked the cable into my house and inside the meter box and found nothing wrong.

Now thinking back to the times that it trips and the times that it doesn’t, things inside the house are being used. It doesn’t seem to matter what is being used but it trips a lot more often when my partner is cooking or watching tv downstairs.

I’ve not managed to keep it on for more than an hour when she is kicking about in the house using things. I also would like to say that it is not being intentionally turned off, someone asked that once and I just want to make it clear now!

So thanks for reading, I will attach some photos of the DB and the meter box.

Lewis
 
Literally it’s connected to the busbar and they is nothing coming out of the top side. It’s tripped three times in the past three days. I can’t make any sense of it. Bear in mind it’s a brand new MCB as well.

Could you post a photo of the consumer unit with the front off
 
The statistical probability of both old and new MCBs exhibiting the same inexplicable fault isn't worth considering, so there's either a rational explanation, human intervention or this thread is destined to enter rather exclusive territory.
Try taking a screenshot of the photos and also crop them a bit if there's any excess around the edges.
 

Attachments

  • 63756DBA-17A4-4526-A67C-911C5503A644.jpeg
    63756DBA-17A4-4526-A67C-911C5503A644.jpeg
    547.6 KB · Views: 75
My money is on human intervention rather than anything electrical.
Haven't looked inside of one for a while, but I take it electronics hasn't found its way into MCBs yet, making them possibly vulnerable to so called smart meters.
We do have a smart meter plugged in, in the kitchen which is the downstairs ring. I’ve had that unplugged though multiple times when trying different things.

There is only me and my partner in the house and neither of us are doing it in purpose.
 
The mechanism inside any MCB that I've dismantled to date is fairly simple, and, if the MCB is in working order, there is no possible way it can be 'tripped', other than by doing what it's supposed to (which it's not, if no outgoing cable is connected), or perhaps by a mechanical shock, such as hitting the side of the fuse box with a hammer.
 
Just to confirm.

the original summer house was experiencing random trips
it was fed from a normal mcb

the board has been changed and the same thing is happening with the new equipment

the outgoing live cable has been removed from the circuit breaker and the breaker still trips at random times.

if all the above is correct, i would be looking for a mechanical reason for tripping as mentioned above by @DPG

I would be considering a covert ip camera watching the board with the cover off and seeing what is going on.

edit,
A video of a breaker tripping on its own with no outgoing cable attached would really amaze me.
if that happens, i would be recommending posting on a forum that follows ley lines, ghosts, spirits, extra-terrestrials, EMF and grounding, etc.
 
Last edited:
In spite of the anticipated reaction and assurances I think a little experiment is due to disprove human interaction before wasting more time on this .

Buy another Wylex B32 MCB (3 or 4 quid)
Swap the B40 for a B32. Don't say a word to anyone but move the sockets on the right to the new B32 on the left (along with the respective neutrals) and connect the summer house to the empty B32 on the right (and move the neutral too). This is all temporary.
See if the the same breaker keeps tripping.

If the problem moves to the right without anyone else knowing then it's an electrical problem that is foxing the finest electricians I know.
If the problem stays on the left I'm afraid it's most likely to be a human interaction issue.
 
Just to confirm.

the original summer house was experiencing random trips
it was fed from a normal mcb

the board has been changed and the same thing is happening with the new equipment

the outgoing live cable has been removed from the circuit breaker and the breaker still trips at random times.

if all the above is correct, i would be looking for a mechanical reason for tripping as mentioned above by @DPG

I would be considering a covert ip camera watching the board with the cover off and seeing what is going on.

edit,
A video of a breaker tripping on its own with no outgoing cable attached would really amaze me.
if that happens, i would be recommending posting on a forum that follows ley lines, ghosts, spirits, extra-terrestrials, EMF and grounding, etc.
I’ll try and get a video on Saturday when I have time, speak to you all then and thanks for your time!
 
In spite of the anticipated reaction and assurances I think a little experiment is due to disprove human interaction before wasting more time on this .

Buy another Wylex B32 MCB (3 or 4 quid)
Swap the B40 for a B32. Don't say a word to anyone but move the sockets on the right to the new B32 on the left (along with the respective neutrals) and connect the summer house to the empty B32 on the right (and move the neutral too). This is all temporary.
See if the the same breaker keeps tripping.

If the problem moves to the right without anyone else knowing then it's an electrical problem that is foxing the finest electricians I know.
If the problem stays on the left I'm afraid it's most likely to be a human interaction issue.
I’ll also try this 👍🏻
 
I’ll try and get a video on Saturday when I have time, speak to you all then and thanks for your time!
You have such an unusual fault, there are a dozen highly trained and experienced electricians here that are invested in your problem and would love to find out what the problem is.
Mystery hunters should be a new member tag for all that have posted there ideas here!!
Our time is given freely but thankyou for recognising it.
 
A few questions.
Did you not carry out a full eicr before the board change?
All new colour cables in your photo - a full rewire at some stage, extended circuits or a newish property?
Knowing you have had on going issues, you chose to fit a dual rcd board rather than an rcbo board (and no spd).
 
I am minded - not yet decided since Carlise is half a day's travel each way - to take a look myself so intrigued am I with this problem.

My suspicions have turned to the smart meter. it contains a contactor which isolates the incoming mains in the event of tampering, end of credit, remote supplied command or loss of incoming mains power. The working hypothesis is that there are very brief complete interruptions in mains power to the output terminals of this smart meter caused by some sort of fault associated with this relay or its control including the meter enclosures anti-tamper circuitry. When there is a a very brief interruption in 240Vac when some non-trivial current is being supplied as would be the case when you and /or your wife are using electrical equipment or indeed when fridges and freezers start or run - then the transient currents which flow briefly after power returns to normal causes very high but short duration pulses of magnetic flux in the short circuit solenoid of the mcbs. These pulses of high current high magnetic flux are interpreted by those circuit breakers passing current as short circuits and thus they trip. Oddly but not physically impossible the sunhouse mcb trips even when it is only connected to the busbar but nothing to its output because the high pulse of magnetic flux(es) from adjacent mcbs link its own short circuit solenoid causing it to trip.

These events are initiated and noticeable only when non-trivial currents are flowing thus during gaming, cooking and the use of high power white appliances.

It is still not certain even though the dno have been and tested(? ) that there is no external fault with the distribution network your home connects to noting it is a PME supply. If it was a street long problem others would be complaining - and they are not - so if there was a supply defect then more probably it would be in the feed to your home. Is your street fed by overhead lines?

Would you please load up the ring circuits and your sunhouse too (so reconnect the fed to it to the B40A mcb) and then take a rolling pin or hammer and tap the smart meter in a number of places a number of times. Obviously don't beat the living daylights out of it as much as most of us would quire understandably want to at 50p a kWh!

After this, please take some small plastic clear freezer bags and aluminium foil. Using an mcb as a template cut out two pieces of ally foil shaped to both sides of the mcb. Place these each in a small plastic freezer bag. Interposed these insulated ally sheets between the sides of the mcbs which usually trip. Wait and see what transpires. Obviously take great care that the ally is inside the plastic and does not touch the busbar. No shame if you think this is too risky for you to do. You really do have to be very careful. I only suggest it because you are a qualified electrician. You are making a Faraday shield. See

Faraday cage - Wikipedia - https://en.wikipedia.org/wiki/Faraday_cage

Also wiggle the meter tails to see if their movement causes the trip.

I recall a smart problem in Birmingham when its radio transmissions interfered with the electronics of the rcd causing it to trip - but your rcd does not trip so we will keep that on the back burner for now.

Is the meter cupboard metal or plastic including the door? Is the mobile phone signal strong where you live? How old is the smart meter in the cabinet?
 
Last edited:
I am minded - not yet decided since Carlise is half a day's travel each way - to take a look myself so intrigued am I with this problem.

My suspicions have turned to the smart meter. it contains a contactor which isolates the incoming mains in the event of tampering, end of credit, remote supplied command or loss of incoming mains power. The working hypothesis is that there are very brief complete interruptions in mains power to the output terminals of this smart meter caused by some sort of fault associated with this relay or its control including the meter enclosures anti-tamper circuitry. When there is a a very brief interruption in 240Vac when some non-trivial current is being supplied as would be the case when you and /or your wife are using electrical equipment or indeed when fridges and freezers start or run - then the transient currents which flow briefly after power returns to normal causes very high but short duration pulses of magnetic flux in the short circuit solenoid of the mcbs. These pulses of high current high magnetic flux are interpreted by those circuit breakers passing current as short circuits and thus they trip. Oddly but not physically impossible the sunhouse mcb trips even when it is only connected to the busbar but nothing to its output because the high pulse of magnetic flux(es) from adjacent mcbs link its own short circuit solenoid causing it to trip.

These events are initiated and noticeable only when non-trivial currents are flowing thus during gaming, cooking and the use of high power white appliances.

It is still not certain even though the dno have been and tested(? ) that there is no external fault with the distribution network your home connects to noting it is a PME supply. If it was a street long problem others would be complaining - and they are not - so if there was a supply defect then more probably it would be in the feed to your home. Is your street fed by overhead lines?

Would you please load up the ring circuits and your sunhouse too (so reconnect the fed to it to the B40A mcb) and then take a rolling pin or hammer and tap the smart meter in a number of places a number of times. Obviously don't beat the living daylights out of it as much as most of us would quire understandably want to at 50p a kWh!

Also wiggle the meter tails to see if their movement causes the trip.

I recall a smart problem in Birmingham when its radio transmissions interfered with the electronics of the rcd causing it to trip - but your rcd does not trip so we will keep that on the back burner for now.

Is the meter cupboard metal or plastic including the door? Is the mobile phone signal strong where you live? How old is the smart meter in the cabinet?
Does the theory still stand when there is no connection to the outgoing side of the mcb ?

Hope it’s not caused by a ham radio station next door 😜
 
Does the theory still stand when there is no connection to the outgoing side of the mcb ?
I wrote - albeit I have edited the text a few times so maybe you did not see it -

Oddly but not physically impossible the sunhouse mcb trips even when it is only connected to the busbar but nothing to its output because the high pulse of magnetic flux(es) from adjacent mcbs link its own short circuit solenoid causing it to trip.
 
A few questions.
Did you not carry out a full eicr before the board change?
All new colour cables in your photo - a full rewire at some stage, extended circuits or a newish property?
Knowing you have had on going issues, you chose to fit a dual rcd board rather than an rcbo board (and no spd).
My house is 7 years old mate and the sun house is just an extension of the old garage, but the cable feeding the garage is the original cable.
It didn’t even cross my mind to fit an rcbo board to be honest mate.
 
I am minded - not yet decided since Carlise is half a day's travel each way - to take a look myself so intrigued am I with this problem.

My suspicions have turned to the smart meter. it contains a contactor which isolates the incoming mains in the event of tampering, end of credit, remote supplied command or loss of incoming mains power. The working hypothesis is that there are very brief complete interruptions in mains power to the output terminals of this smart meter caused by some sort of fault associated with this relay or its control including the meter enclosures anti-tamper circuitry. When there is a a very brief interruption in 240Vac when some non-trivial current is being supplied as would be the case when you and /or your wife are using electrical equipment or indeed when fridges and freezers start or run - then the transient currents which flow briefly after power returns to normal causes very high but short duration pulses of magnetic flux in the short circuit solenoid of the mcbs. These pulses of high current high magnetic flux are interpreted by those circuit breakers passing current as short circuits and thus they trip. Oddly but not physically impossible the sunhouse mcb trips even when it is only connected to the busbar but nothing to its output because the high pulse of magnetic flux(es) from adjacent mcbs link its own short circuit solenoid causing it to trip.

These events are initiated and noticeable only when non-trivial currents are flowing thus during gaming, cooking and the use of high power white appliances.

It is still not certain even though the dno have been and tested(? ) that there is no external fault with the distribution network your home connects to noting it is a PME supply. If it was a street long problem others would be complaining - and they are not - so if there was a supply defect then more probably it would be in the feed to your home. Is your street fed by overhead lines?

Would you please load up the ring circuits and your sunhouse too (so reconnect the fed to it to the B40A mcb) and then take a rolling pin or hammer and tap the smart meter in a number of places a number of times. Obviously don't beat the living daylights out of it as much as most of us would quire understandably want to at 50p a kWh!

After this, please take some small plastic clear freezer bags and aluminium foil. Using an mcb as a template cut out two pieces of ally foil shaped to both sides of the mcb. Place these each in a small plastic freezer bag. Interposed these insulated ally sheets between the sides of the mcbs which usually trip. Wait and see what transpires. Obviously take great care that the ally is inside the plastic and does not touch the busbar. No shame if you think this is too risky for you to do. You really do have to be very careful. I only suggest it because you are a qualified electrician. You are making a Faraday shield. See

Faraday cage - Wikipedia - https://en.wikipedia.org/wiki/Faraday_cage

Also wiggle the meter tails to see if their movement causes the trip.

I recall a smart problem in Birmingham when its radio transmissions interfered with the electronics of the rcd causing it to trip - but your rcd does not trip so we will keep that on the back burner for now.

Is the meter cupboard metal or plastic including the door? Is the mobile phone signal strong where you live? How old is the smart meter in the cabinet?
Feel free to come to Carlisle mate 😂 you’re most welcome to. I’m currently at work and I have tomorrow planned in for trying things. So I will do as you have asked! I will get the info you have asked for tonight though.

Again thanks for your time in this 🙏
 
When there is a a very brief interruption in 240Vac when some non-trivial current is being supplied as would be the case when you and /or your wife are using electrical equipment or indeed when fridges and freezers start or run - then the transient currents which flow briefly after power returns to normal causes very high but short duration pulses of magnetic flux in the short circuit solenoid of the mcbs.
While that sounds plausible in theory, I really doubt any home system is going to produce that big a magnetic field. Indeed if it did, I would expect to see bent steel enclosures!
 
While that sounds plausible in theory, I really doubt any home system is going to produce that big a magnetic field. Indeed if it did, I would expect to see bent steel enclosures!
Noted.

To fathom this problem I am being creative in generating the hypothesis to inspire the next line of diagnosis. I can see myself visiting.............

I am more open minded about extraordinary current waveforms of several hundreds of Amperes and short duration with their associated magnetic field/flux. Quirky circumstances causing resonance perhaps and not necessarily at 50Hz but a harmonic or several of them?

I don't care if I am wrong.
 
Last edited:
Even short-circuit currents of many kA do not trip adjacent MCBs. I could ask a friend who has a large magnet-charger (i.e. huge electromagnet) to try tripping an MCB with it.
 
In spite of the anticipated reaction and assurances I think a little experiment is due to disprove human interaction before wasting more time on this .

Buy another Wylex B32 MCB (3 or 4 quid)
Swap the B40 for a B32. Don't say a word to anyone but move the sockets on the right to the new B32 on the left (along with the respective neutrals) and connect the summer house to the empty B32 on the right (and move the neutral too). This is all temporary.
See if the the same breaker keeps tripping.

If the problem moves to the right without anyone else knowing then it's an electrical problem that is foxing the finest electricians I know.
If the problem stays on the left I'm afraid it's most likely to be a human interaction issue.
This is the next thing that should be done. See if the fault stays with the MCB or moves with the circuit.
Same technique is often used to sort a misfire on an engine. Move the ignition coil or the injector, and see if the fault follows the component or stays with the cylinder.
 
@marconi I've driven from Eastbourne to Carlisle several times having lived in both places. Granted once was in an LDV Pilot with a cat and a 2 year old for company which is a combination of vehicular technology and company I never want to do again. Whether the differential or the cat made more noise is open to debate. But my point is that if it were me I'd want to rule out human intervention before travelling.
(But if you do go to Carlisle - I'd suggest you'd enjoy a visit to Bookcase on Castle Street which is the best 2nd hand bookshop spread over many floors I've ever found, all properly organised like a library)
 
@marconi I've driven from Eastbourne to Carlisle several times having lived in both places. Granted once was in an LDV Pilot with a cat and a 2 year old for company which is a combination of vehicular technology and company I never want to do again. Whether the differential or the cat made more noise is open to debate. But my point is that if it were me I'd want to rule out human intervention before travelling.
(But if you do go to Carlisle - I'd suggest you'd enjoy a visit to Bookcase on Castle Street which is the best 2nd hand bookshop spread over many floors I've ever found, all properly organised like a library)

I'd wager the cat was significantly more responsive than the steering in that LDV.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Carlisle
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)