I agree that it's a poor design and have disconnected in the past the extra spur due to, more than one spur from the MCB seeming wrong due to it being non standard, but thinking about it afterwards i couldn't quite explain to myself why it was wrong, it. Only it being a poor design and non standard, but otherwise it wasn't unsafe. It reminds me telling a friend, when asked if it was wrong with doubling up the conducors on an undersized flex feeding a fixed item of equipment. I told him it was but then stumbled on explaining why it couldn't other than it being yee hawish and possibly the CPC being undersized. I suppose it's all food for thought.This is what I would call a pathological configuration that is specifically designed to be difficult to analyse in the terms set out in the regs.
An unfused spur on an RFC bypasses the convention Ib<In<Iz due to the downstream protection afforded by the load being a single BS1363 point (although, not full protection for cable with Iz=20A which are permissible on an RFC.) The defined format of the RFC and its spurs have been proven safe and effective in practice over 75 years of use.
The two-point centre-fed radial then tries to exploit the same idea in a situation that is not an RFC nor a defined standard circuit in BS7671. Therefore, while it should be no more or less safe electrically than two unfused spurs (although there are aspects of anticipated load to consider according to application) there are better ways of feeding two points that don't depend on that exemption adopted into the RFC.