Hi,
We are renting and have a electric shower downstairs (extension) - a 9.5kW Triton T80Z fast-fit electric shower as well as a combi boiler Viessmann Vitodens 100-W B1KC 35 kW. Upstairs is a standard shower/bath direct from boiler.
Our family members tend to use the downstairs electric shower and have been recently complaining about the water pressure. We are well aware that if any water outlet is being used in combination then there is a drop in pressure at both ends - for whatever reason. This has occurred at times when only the shower is being used though. I performed a approximate water pressure test using a 1L jug and a time of 6 seconds, results where when the electric shower heating element is essential off not operational i.e. cold then the pressure is 7.5L/min @ 0.75 bar. When at a reasonable temperature it is 6L/min @ 0.6 bar.
The electric shower is rated for 8L/min @ 1 bar. So I guess we are slight off?
The main query is whether there is anything that can be done to increase the water pressure, I read that due to having a combi boiler a water pump isn't possible, hence the electric shower route I'm assuming?
Also would an upgrade to the 10.5kW version with everything as is just a swap out make any difference as it's rated with a higher flow rate? I am aware that a new electric cable may need to be fed depending on the current setup however if there would be no improvement due to being bottle necked by the water pressure there wouldn't be a point.
Appreciate any help/advice.
Your water pressure probably isn't the problem here.
(Assuming you are always using the high setting rather than economy) the shower element heats at a set output, this doesn't change. When you turn the dial to adjust the temperature, you adjust the flow rate of water: the slower the water passes over the element, the more heat it absorbs, and so the warmer it will be when it leaves the unit.
So a particular water temperature should always have a corresponding flow rate (all other things being equal. For example, in winter the water entering the unit will be cooler, so would need to spend more time with the element to heat up to that particular temperature).
I assume you're using the shower on the high setting rather than economy? It may be that one of the elements has died, so it's not heating the water fast enough, and you have to lower the flow rate to compensate.
Alternatively, it may just not be living up to expectations, and maybe a 10.8kW shower would be better.
The regulator in the shower could be on its way out too, (the temp dial), not common but agree with other suggestion that common water supply or you're close to industrial or commercial with regular demand that could drop pressure, this would result in the shower getting hotter yet less water output.
Is the cold tap pressure ok in the bathroom where the shower is? Where the shower connects to the cold water pipe there is often a filter in the incoming tube.If grit from the water starts to clog up the filter then the water pressure will reduce.Might be worth checking the filter(if there is one).
One query I have here is why, when you have a combi boiler, do you have an electric shower downstairs?
Most combi boilers,in my experience, output enough pressure for a shower of the normal type having hot and cold inputs.
A purely electric shower is useful in case the boiler fails, or if it's tricky to plumb it in to hot and cold supply, but that is unusual. Assuming the pressure is fine at the main bathroom, I suspect it's a low cold water pressure overall that is the problem. I say this because the OP suggests it is the flow rate that is the problem, not the temperature. There are other solutions if the flow rate is the only problem.
It's impossible to know your complete set up, but if you are sharing water mains with a neighbour then everything they do will also affect the pressure. This could explain why pressure drops for no reason when you're not using anything and somebody is showering.
I have fitted these before now in cases like yours and they work well. HomeBoost Mains Booster Water Pump | Salamander Pumps - https://www.salamanderpumps.co.uk/products/mainsbooster/homeboost/#compatibility
I don't believe we are sharing water mains with a neighbour, we have our own water meter in our front drive. It's a mid-terrace property.
Just had a look at the link, why do companies (Viessmann) state combi boilers aren't compatible with water pumps yet this states it's compatible with a combi boiler? I will do a check on our other taps and upstairs shower in terms of flow rate, as it is generally "stronger" than the electric shower. As this unit is fit essentially directly onto the boiler there may be little to no benefit of the boost of advertised (12L/min) if the house is already getting close to that but the electric shower being an isolated case if that makes sense.
Yes shower is generally being used on high setting mode instead of economy mode however even on high setting mode the temperature dial would only be set to about 50% as 100% is almost kettle temperature. Aware the hotter you put it the slower the water trickles through. However was wondering whether as on cold we are only getting 0.75 bar whether there are gains of 0.25 being lost somewhere/make much of an improvement? As on cold no heating elements are used therefore no bottleneck, should be a straight flow through.
I will have a go and experiment with the settings again, good point about a potential heating element being bust, would there be a way to test this? I believe the unit is dated 02/14, most likely manufactured date however it most likely is 3-4 years old now?
Is there a way to test this/isolate the problem?
We have a sink in that bathroom and the flow is the same as elsewhere in the house. Just the shower being an isolated issue. However will check flow rates on all the taps just to get an idea. Will also check your filter suggestion as not sure whether one is present will check in the manual.
According to some research prior to posting here it is quite common practice for a second bathroom (no clue why just what I read)? We have an upstairs main shower regulated by the boiler. The house had an extension whereby for the 2nd bathroom now a electric shower was installed. The boiler itself is situated literally 4m from the electric shower (small utility room next door) so running pipes would have been easy.
Judging by the extension workmanship lets just say a lot to be desired, I wouldn't be surprised if everything was just done on the cheap and ASAP.
Looking back at your original post, you say there have been complaints about "water pressure". I don't quite understand what this means.
Do they mean that the water flow rate is insufficient at a normal showering temperature? If so, this is nothing to do with water pressure, and is the result of a faulty shower, an incorrect shower head having been fitted, or unrealistic expectations of electric showers.
Yes the flow rate being lower on normal showering temperature. The advertised specs for electric showers what sort of temperature range are they based on (asking as nothing seems to be specified anywhere)? i.e. 8l/min @ 1bar for a 9.5kW, if that's the output on cold water sure (in our case), but on the max it would be half that even less if that makes sense.
The only thing I can think of is run it on high setting, then change down to economy setting and see if there is any difference in the water temperature.
If no difference in temp, then I'd expect an element has gone completely. If it runs cold, without any heat at all in economy, then I'd also expect an element to have gone. If it is noticably cooler in economy setting, but there is some heat, then I'd expect the elements to be working as they should be.
Electric showers follow a simple equation: Power input = flow rate x temperature.
Rearranging, temperature = power input/flow rate, so, if the temperature is correct and the flow rate is low, the power input must be low as well.
As above, the flow and temperature you get from an electric shower is determined by the laws of physics.
Mira published the graph below to illustrate the performance of their showers.
(from this publication: https://www.mirashowers.co.uk/media/1453/miras-guide-to-electric-showers.pdf)
Assuming cold water is coming into the house at say 15 degrees, and you like a nice toasty shower to be at 40 degrees, you need the shower to heat the flow of water by 25 degrees.
The graph indicates that to achieve a flow of 6l/min, you need at least a 9.6kW shower element.
The original post #1 suggested the shower is rated at 8l/min at 1 bar. That may be the max flow you can get out, but the rise in water temp you would get from a 9.8kW shower would be about 18 degrees, so would feel cool! If you then compensate by turning the shower temperature up (which just reduces the flow) you would be down to about 6l/min to get a comfortable temperature.
From the OP's observations I am wondering if the shower is actually performing more or less consistently with the graph below?
If so, maybe the conclusion is that a more powerful shower would improve everyone's showering experience!
Pretty Mouth's tests that I quoted above will determine if both elements are working, and if they are, it's likely that the problem is just unreasonable expectations.
I've also had the odd complaint of poor electric power flow which turned out to be tht the supplied shower head had been replaced by one intended for showers fed from a hot water system. Electric showers give the illusion of flow by using very fine jets in the head. If this is replaced by a head with larger jets, you get to see how poor the flow really is.
Is scale a problem where you live (ie hard water). De-scaling the unit/hose and head can often make it seem like new!
Yes we do have a bit of a scale problem but nothing serious. Yesterday I took the unit apart, and checked the piping also the filter and they are spanking clean, 0 signs of any scale. When initially performing the flow test I tested it with the shower hose and head and also without i.e. just directly from the electric shower itself just to try and rule out any bottle necks with the hose/head.
Tested this yesterday, put it on economy mode and about 80% temp turn and that's a reasonable heat although very poor flow rate in comparison to max/high mode and about 60% temp turn for a bit of a hotter heat.
Will take a look at the link and graph appreciated.
I personally rarely use the electric shower downstairs but have previously and to me it worked fine. However after the complaints from family members thought I'd investigate.
________________________________________________________________________________________________________________________________
To add I wanted to check the whole setup and cabling. So I did yesterday and to me it seems like a possible cowboy installation? As trying to figure if installing a higher kW unit would be possible but it wouldn't with the current cabling. I'm dubious if even the current setup is appropriate and not currently overloaded!
So we have the 9.5kW electric shower which is using a 6mm cable connected approximately 1.5m through the wall going to a isolating switch outside the bathroom (switch between the electric shower and mainboard power panel). This then feeds through the kitchen going to the utility room just outside under the stairs into the mainboard this is approximately a further 5.5m so total of 7-8m of cable. It's fused to a Crabtree B32 61 MCB breaker (rated 32A?).
The 9.5kW unit according to the manufacturers spec should have a 40A breaker? Heck even the 8.5kW needs a 40A unless I'm not understanding something along the lines. The 7.0kW/7.5kW would of been fine for the 32A and 6mm cable.
I have also read conflicting views elsewhere whether a 6mm cable under a certain total length is suitable as a replacement for a 10mm under certain conditions?
So now I'm wondering whether enough power is even being delivered to the unit to operate at it's full potential? Or would the unit not operate at all otherwise?
An undersize cable would not affect the power delivered to the shower on such a short run, and a 'poor connection' would quickly show itself by burning out the joint and cooking any insulation present.
I'm fairly convinced that what we have here is an expectation that an electric shower will be a match for a well installed conventional one, which just isn't going to happen.
Could the issue simply be one of urealistic expectations from family members comparing one shower with the other?
I feel the same after spending time in a hotel, then returning home to less than desirable water pressure.
Hi,
How are you measuring the water pressures of 0.75 and 0.6 bar?
a flow rate of 6 litres per minute should be enough for a shower. Are your family members used to a high rate of flow from a power shower in a previous property?
I have a TZ80 10.5 kw shower in 2nd floor bathroom. Just used it and measured clip flow rate. I get 1 litre in 10 sec, 6litre a minute. we find that fine. Not measured flow rate when hot. Electrical Power is on the lowest of the two settings. I suspect could increase rate of flow by opening the main stop tap more … it’s not fully opened, but I’m happy with the flow rate.
Main stop cock of any property should be fully open, less a few degrees to help stop it sticking. Flow rate to any individual appliances should be controlled by its local isolator.
@Dave1UK Are you certain that the shower head in use is the one that was supplied with the shower?
Unfortunately can't be 100% sure as it's a rented property.
As per below method:
I ran the test several times and same results throughout.
_________________________________________________________________________________________________________________________________
Anyhow I have spoken to my family members and they all agreed, going to go ahead and buy a new unit like for like replacement. This unit is definitely few years old 4+. They are aware it may be an improvement or no improvement at all, guess will have to bite the bullet on this. As it will come with the shower head meant for the unit as well that would resolve that. Will update the post as soon as that is done and report of any improvement if any. Appreciate all of the advice from everyone!
Can't imagine too many landlords would offer to replace a working shower.
It doesn’t work though.
If the pressure used to be good, now it’s not…. Then there’s a problem.
It needs looked at properly. What’s the point of getting a new shower if there’s a blockage elsewhere in the pipework as some have suggested.
No harm in asking.
Your landlord should be replacing it, not you.
No harm in asking.
Doesn't matter - a tenant should not be changing things like showers without permission.
We are on good terms with our landlord, the rent we are paying is extremely fair in comparison to rents in our area. Landlord hasn't hiked the rent up either (over 2 years). Spending a bit here and there on the house upkeep especially on things/appliances which I personally view as wear and tear appliances isn't an issue - of course there is a limit, I wouldn't be paying for a new boiler. Also considering we plan on renting here long-term (few more years at least) of course landlord could change their mind tomorrow but it is what it is.
Landlord is made aware of any issues, if it's something I can manage I go ahead, if not I tell them to call in someone. I personally document all the work as well, i.e. issues/before photos/after photos/receipts etc. Not that I foresee it but I see that as bargaining chips if discussion of rent was to ever come up.
It’s an unusual, but wholly positive arrangement you have with your landlord.
We tend to get a lot of nightmare story’s on the forum of landlord that don’t give two hoots about tenant safety, and many of us jump to conclusions that the landlords in question are shirking doing the work.
I’m happy to learn otherwise here.
But I will advise not to blindly upsize the power of the shower without first checking the circuit is up to it… this includes the breaker, cable and isolator switch
No harm in asking.
It does work and OP isn't even certain that anything is wrong - just that other family members aren't happy with water flow
That's another matter entirely.
If both elements are working (which I think has been proven) and the water temperature is correct, and adjustable around that correct point, then the flow MUST be correct. Anything else would defy the laws of physics.
If the flow is correct, and you don't get an acceptable spray pattern, then a head has been fitted with too many holes, or holes that are too big.
Yeah if I was paying a high premium for rent like unfortunately some others then I sure would expect to be getting a top notch kitted property and landlord on speed dial to be honest. I think it's a fair trade off otherwise.
I wouldn't be upsizing, would be a like for like replacement, they still produce the same unit and model with same power rating. I previously mentioned on my post (quite bit of a read now) that I checked the power cables and fuse and they wouldn't be able to support a higher power rated unit unfortunately without an upgrade (the cabling would be quite a bit of work not worth it). Good advise though.
Everything seemed fine to me when testing but then again I don't use it on a day to day basis, it is possible the heating elements may not work intermittently? Can't be 100% positive, in terms of the shower head it would be a good £20-30 for a branded replacement. A new unit complete set is around £240ish? £200 extra is a lot but it would rule out heating elements and either way we have all agreed to share the cost of it so it dampens the cost down even further.
Guess we will see.
, it is possible the heating elements may not work intermittently? Can't be 100% positive, in terms of the shower heade.
The heating elements are switched by pressure switches inside the unit. These pressure switches are down wind of the flow controller, so can be affected by a head providing insufficient flow resistance (too many or too big holes), resulting in insufficient back pressure to work them reliably.
You can discount poor connections in any component affecting the element's power. Very high currents in a very small space will soon give themselves away by heat damage if there's any resistance where there shouldn't be.
So went ahead and purchased a new unit few days ago, surprisingly wasn't as expensive as I initially saw online £120.46 delivered.
Got a chance to fit it yesterday and everything works as it should and after being used yesterday by a family member they said the pressure is much better and also temperature wise its stable.
The old unit was indeed correctly dated as 02/14, as the new one received is dated 06/23. So guess give/take few months.
Also the shower head on the old unit wasn't the original one, so it's possible that could have/played a part.
All in all, guess it worked out. A new shower head replacement may have been enough as advised by another member here however no harm in future proofing with having the whole unit replaced especially at that price point, age of unit etc.
Thanks for letting us know. I think you made the right choice to be honest.
London
Electric Shower Pressure Query
Dave1UK,
DPG,
