Aug 3, 2023
Glasgow
Morning,
Company had an external contractor coming in to complete an EICR recently. They have gave us the report with a C2 for holes in trunking at high level. For reference, this trunking has been pre-drilled with 20mm holes at set distances on either side. Within this trunking is multiple single core and multicore cables but no live parts. Personally, I think it's overkill but not had a lot of experience with test/inspection coding.
The main tester on site has also recently became director of the company so I may be thinking cynically that he was merely trying to provide easy work for his business
Most people will Code 2 this if single insulated conductors are exposed. The fact it is high level is not relevant as you cannot use out of reach as a means of protection in most general installations.
That’s fair enough. Just wanted a second opinion on it so cheers for that
A bag of 20mm blanking plugs will sort it. Easy fix
dont even need to open the trunking.
That’s exactly what we are doing as speak haha! A ball ache but an easy job. 300 down and not even half way yet😂
Access to single insulated cables without the use of a tool. Oooh I'm in a mischievous mood today:-)
  • Funny
Reactions: nicebutdim and ferg
Access to single insulated cables without the use of a tool. Oooh I'm in a mischievous mood today:)
Would that mean any consumer unit with plastic push in blanks is not compliant ? Or a wago jb.
Wago JBs should have a cable tie fitted through the loop provided. This needs cutters to remove it.
I maybe wrong, but I think that's only when used MF there are many junction boxes that have clip on lids, but wouldn't be compliant for inaccessible locations
No, you can use the cable tie feature any time you use a wago box, regardless of whether you need it to be MF or not. And then it needs a tool to open it.
You MUST use the tie to be MF compliant, but you don't have to use it when used in accessible areas.
As already said, there are many Junction boxes that can be opened exposing single insulated cables that can be opened without the use of a tool, including single push in blanks in a DB.
I was just replying to your example of a wago JB not needing a tool to open it.
Accessible areas which require a tool to access?
I was on about wago Mf jbs needing the tie to be compliant when used as MF, but not having to use it when it's accessible.
It's all confusing, time for another southern comfort.
Reactions: DPG and loz2754
Yeah I think you might have missed my point. No worries, might have a little snifter myself. Cheers!
Would someone be so kind as to give me a Reg No. for this?
"521.10.1
Non-sheathed cables for fixed wiring shall be enclosed in conduit, ducting or trunking.
Non-sheathed cables are permitted if the cable trunking system provides at least the degree of protection IPXXD or IP4X, and if the cover can only be removed by means of a tool or a deliberate action."
The last bit about deliberate action is a little vague in its intent...
Reactions: DPG and nicebutdim
Glasgow
Pre-drilled holes in trunking EICR Code
indspark23,
Avo Mk8,