Nov 29, 2023
South London
Hello All
So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems. I have a three phase switch fuse Isolator rated at 200Amp supplied by the landlord. I need to split this across two Proteus distribution boards, the main switches and Busbars are rated for 100 amps 3 phase. I need the full 200amps so I can't just swap the fuses out in the Isolator. So my question is... between the boards and Isolator how would you go about fusing down? A 6 way ryefield, 100 per phase?
Three phase or single phase Proteus boards?
Three phase
I reread your first post and realised. Are you sure they aren't 125A?
If you need the full 200A and have space just install additional switch fuses.
Reactions: pc1966
Can you fit a 100A MCCB incomer to those Proteus boards?
If so just make sure all the cable up to each board's incomer is rated to clear the 200A fuses.
I see 3 options.
4 way to mccb panel
Ryfield unit
or bus bar chambers with 2x 100 amp switch fuses or with some DBs you can fit a mccb to use as the main switch. Schieder is one example I know of.
Reactions: pc1966
Wow a few options coming at me here.
Sooo MCCB option, seems like a viable idea but then I'd need to bolt 2 sets of 95mm tails to the switch fuse unless a busbar chamber is used?? In which case we may as well just fit one 95mm tail and use fuses in the chamber?
Please forgive my lack of knowledge on commercial, I'll try to keep up!
First you need to see if you can get MCCB incomers - a quick look at the CEF site for Proteus was not too hopeful (only seem to have isolator switches), but worth asking them for that.
Next big point is how far is each TPN board from your 200A switched-fuse? If it is a short distance then it is reasonable to use incomers (if available!) and 200A cable, but if a significant distance to one or the other then fusing down at origin is a better plan.
As @Flanders suggested you can do the split in several ways: MCCB boards are good for complicated set-ups and if unskilled people might have to reset a breaker, but fuses in the form of a pair of switched-fuses or a small Ryfield board are often cheaper and have a better trade off in terms of operating current versus end of cable Zs to meet 5s disconnection (assuming TN here).
Reactions: Flanders
So my set up is all confined to a small intake room where you couldn't even swing a piece of conduit at the apprentice. I have a roughly 800mm length of 4inch trunking with the Isolator on top, the main dB to the right and a 500mm space between the board and Isolator on top of the trunking for a Ryefield. This seemed like the easiest option and one which I've has experience with! Cost the factor which has lead me here.
I doubt Proteus do 947-2 incomers.
Reactions: davesparks
Why the two boards are they metered separately?
No, you'd only need one set of conductors from the switchfuse to the MCCB distribution board, then suitably sized outgoing conductors from each MCCB.
I had to do pretty much the same thing on this job, take an existing 200A feed and split it down to 2x 100A feeds. Previously the fuses in the fuse-switch had been changed to 100A to feed the one outgoing distribution circuit. I needed to add a second distribution circuit so swapped the fuses back to 200A and fitted the MCCB board.
(Yes I fixed the gap in the trunking lid)
The board is an MG25C2 Scheider Merlin Gerin MG25C2 Powerpact 4 - 13 SP Ways, 250A Panelboard - https://electricalwholesalers4u.com/products/scheider-merlin-gerin-mg25c2-powerpact-4-13-sp-ways-250a-panelboard?variant=44704876888310&utm_source=google&utm_medium=organic&utm_campaign=Shopify%20Custom%20GMC%20Feed&utm_content=Scheider%20Merlin%20Gerin%20MG25C2%20Powerpact%204%20-%2013%20SP%20Ways%2C%20250A%20%20Panelboard&gad_source=1&gclid=Cj0KCQiA35urBhDCARIsAOU7QwkSOymDJNpGhIUA29hoH4fm2Mx-5DhK5dkP9ueAsGsdRUrUqr7CY-MaAksFEALw_wcB
The easiest option isn't necessarily the best option and the cheapest option is rarely best.
Fuses vs MCCBs both have their pros and cons.
MCCBs offer convenience of being easily resettable.
With the Ryefield option the whole installation would need to be isolated to replace 1 fuse (removing/reinstating fuses into a live board is hard to justify in a risk assessment without a good reason and expensive arc-flash PPE)
Very true!
As there is a 200A fused-switch feeding it then easy to do, and if 100A fuses feeding the TPN boards they should be no more likely to be blown than typical house DNO fuses, and will have total selectivity with the 200A ones.
Assuming sensible distribution of loads, overall demand, etc.!
Don't forget that 434.2 allows for positioning of the over-current protection to be downstream of the device where downstream protection exists (so your MCCB incomer). As such, you may only need 35mm tails which the vast majority of switchgear would accept being double-lugged (normally one behind and one in front of the bus bolt).
Reactions: pc1966 and James
Why the two boards are they metered?
Whilst maximum demand of the 100 amp main switch is just tetering on exceeding the rated current (and I don't think I can get anything larger than 125A for Proteus) I also need a HVAC board and contactor linked into the fire detection to kill the hvac board in the event of alarm activation.
Eaton MEM EBMSL14102MPMB 14+10way 200amp TPN Split Metered Power and Lighting Board would this board work for you
There has been some great feedback here guys and all sooooo helpful! All my boss wants to do is quickly me along and cheap cheap cheap! With absolutely no understanding where he's been off the tools for so many years!
So ive taken all of your knowledge and suggestions and think ive decided on an engineering judgment on how I'm going to move forward on this project!
1 - 434.2 is gold here because well... I really don't want to work with cable bigger than I really have to!
2 - MCCB Incomers - Ive never had to consider before and this allows me to comply with the above whilst protecting my DB main switches
3 - I can be cost effective in that two separate MCCB enclosures is apparently cheaper than the Ryefield (which is about a grand according to the boss)
4 - I can be time effective in that making all the links for a Ryefield is time consuming. (im sure you can probably buy somthing prefabricated)
5 - I will use a 100amp MCCB Incomer for the HVAC DB, a 125 Amp for the Main DB
You have all been absolute stars and a great response for my first posting here! Ill have to grab pictures of the final product!
Play safe out there!
Photo of existing and sketch plan of required would be useful.
Like to see this busbar chamber.
One of the things that I have always loved about this forum (above many others) is the breadth of experience and knowledge and the willingness to share that, especially when trying to solve a genuine problem. You’re welcome!!
Unfortunately im having issues uploading these pictures from the phone where the file is too large... Id love to show you!
Here we go! I tried changing the quality at first which didn't work!
Reactions: nicebutdim
Easy enough to do yes, but that does mean shutting down the whole installation which may be more problematic.
My comments were based on not knowing if this was 2 DBs adjacent to the incomer or 2 remote DBs fed by distribution circuits.
Plus Proteus do have a reputation for making less than reliable DBs.
Reactions: pc1966
Here's some kind of sketch to give you guys an idea. Not exactly to scale
Happy new year all!
Furthering my dilemma... This site is due to open to the public in a couple days time and I'm told that an energy meter will not be installed for a matter of weeks. Now as the meter will most likely be CT arrangement there is nothing physically stopping me going to the main intake and switching my install on. Where does this leave me legally though? The theft act of 1968 section 13 says that dishonesty is the key factor in proving the offence. Soooo if there is no meter then we cant honestly monitor the amount of energy used and therefore cant be charged accordingly.
IDK guys
What's your thoughts?
  • Optimistic
Quite Simpley
No,No, NO.
you are not authorised to connect anything to the service head.
if the energy supplier won’t budge and can’t provide a supply before you are due to open then the only realistic option is to hire a temporary generator.
I'm confused. You started the thread talking about what was made to sound like a commercial install, then it changed to include a landlord and now the narrative is one of gates and public. What, exactly, is the nature of this installation?? And no, you can't just energise without a meter as it's not your energy.
Quite Simpley
No,No, NO.
I'd imagine the penalty for dishonestly drawing 200A from a 3ph supply would be significantly greater than for stealing electricity in a domestic setting. I'd also imagine the chances of being caught are also significantly higher.
In the OP's case they are suggesting their own meter, presumably MID-compliant, until the official meter is installed so it might fail the test of dishonesty for any prosecution as they would be measuring and intending to pay for the usage.
I suspect it would still cause so much legal headache it is absolutely not worth doing!
It wouldn't meet the legal test - it would be no different to taking money from a till and leaving an IOU note in it's place.
oh, i never spotted that they intended to install there own meter.
but, regardless it is in my opinion a BIG NO WAY.
the issues and grief involved could be huge.
Sooo the client has accepted that we don't want to be fraudulently taking electricity so that worry is out of the picture. But now basically the supplier and UKPN are now suggesting that we are to install a CT chamber somewhere adjacent to the switch fuse as seen in the photo, Is this normal? Will a meter just plonked on the wall with stuffing glands going into the switch fuse for the CTs not suffice??? why all this hassle? I'm really confused
South London
3 Phase Distribution Board Dilema
Commercial Electrical Advice
SparkingMad1997,
SparkingMad1997,