Today I was doing an EICR and went around a couple sockets with a Megger MST220 socket tester just to see if there was anything obvious, all three green lights came on saying everything was fine and correct. When I took the faceplate off to do my R1 R2s I got readings of 0.60 on R1 but then >2000 on Rn. I know socket testers shouldn't be relied on and I only use it to see if there if anything obvious before I take the faceplate off but surly it should of shown a natural fault?
I mainly use it to plug in to see if there is anything obvious before I go taking the faceplate off but a 0.60 and >2000 I thought it'll pick that up no problem and being a Megger
I have actually emailed Megger to see what they say... I am expecting a 'Don't rely on them' Kind of answer though.