Nov 29, 2018
London
Hi All
Wonder if someone can give me a little advice on a burnt out socket I’ve found today:
Socket has now been isolated at the fuse board and is on a small ring with only 2 other sockets and a 30amp rcd.
Items plugged into the socket were a tp-link smart plug, with a lamp connected to it, and a 4 way extension lead with an Amazon firestick and a wireless router bridge connected. So nothing pulling significant loads.
Socket was installed about 10 years ago and there haven’t been any issues, that I know about, since then. We’ve recently had an extension built which involved replacement the fuse board (new FuseBox model).
Whilst I suspect it most likely that the issue was the live connection in the outlet, which is what has burnt, it feels like potentially too much of a co-incidence that this has happened just a few weeks after the fuse board was changed having been fine for 10 years.
Could the new fuse board have caused something to change here which has resulted in the socket burning out?
Thanks in advance for any assistance
Alex
Reactions: TimJ01
whatever was plugged in there will be damaged as well....
Coincidence... unless they removed that socket for some reason when they changed the board.
Its been a loose cable, and the heat caused by arccing.
You said it wasnt a big load... so im surprised its caused that much heat.
Im surprised you didnt smell it.
The back box appears to be only a 25mm deep one... A lot of decorative metal sockets ask for a 32mm.... maybe the live cables were close to the back wall of the box?
Did you mean a 32A, 30mA RCBO? or a 32A MCB with an upfront RCD mainswitch? (photo?)
Its a simple enough fix, but maybe beyond a DIYer.
Littlespark has said it all before I finished, but I'll post anyway - these were my thoughts:
Has the advent of the extension resulted in additional loads being used on this particular circuit?
Or, for example, have you been using electric heater(s) on this circuit since it's got colder recently?
The socket is on a ring circuit, so a current of up to 10 or more Amps could be trying to flow through the connection between those two (burnt) brown wires (irrespective of whatever is plugged into that socket). The (L) screw terminal in the socket is responsible for maintaining a good connection between the brown wires, and quite clearly it hasn't done the job well, probably not having been tightened to the required torque in the first place.
This fault should have ben identified during the fuseboard change, if it was present at that time.
Have you got documentation from that work that gives figures for the ring circuits?
Excellent thanks and definitely did smell the burning and that’s what directed me to this socket - perplexed as to why the fuse in the consumer unit didn’t trip though?
Builders didn’t touch anything in this room, unless they potentially took this socket out as part of the NIC testing, so must just be coincidence.
I didn’t think it was likely to be anything fuse board related but so strange that nothing for 10 years and then this happens 6 weeks after the fuse board is changed though!
Photos of fuse board attached
The socket is on a ring circuit, so a current of up to 30-odd Amps could be trying to flow through the connection between those two (burnt) brown wires (irrespective of whatever is plugged into that socket). The (L) screw terminal in the socket is responsible for maintaining a good connection between the brown wires, and quite clearly it hasn't done the job well, probably not having been tightened to the required torque in the first place.
Thanks and very much appreciated
Loads on this circuit unchanged - it’s 3 double sockets that serve the media/av setup (sky box, led tv av receiver, router, and a couple of lamps). If anything it’s reduced as we haven’t got a fan connected to it anymore.
Haven’t had the NICEIC cert through yet - have chased up.
I would have thought something like this would have caused the RCD to trip though?
There's no excess current flowing, just your normal (fairly light) loads. A high resistance joint has developed in a wire feeding the various items round the ring, so some watts of energy (heat) are generated, and this tends to be a runaway situation - heat increases the resistance which generates more heat etc. until something gives!
An RCD won't trip until there is an imbalance of current in L and N, and there's nothing here to create that imbalance unless a stray burnt wire develops a leakage to earth, which doesn't appear to have happened, or touches the metalwork, which would trip the MCB as well! (Or as Mainline has mentioned below - RCBO in your case!)
This sort of scenario is what the arc fault detection devices (AFDD's) were aiming to tackle, that are now mandated in various situations, but which don't seem to be attractive to many. 🤔
If it's the one that is switched off saying lounge sockets it's a 20amp rcbo so maybe not a ring final unless it's been downgraded for some reason.
Reactions: Avo Mk8
Hi Both
Many thanks for your feedback on Friday - much appreciated.
Electrician came out on Saturday morning and replaced the socket so all is now repaired.
I've also now received the EICR cert and all was seemingly good on the day the test was done (photos attached) which is even more strange.
It doesn't look like this is a ring main circuit (as mainline correctly spotted) which I assume is why these sockets have two live and two neutral wires to each terminal - would this setup make these sockets more susceptible to an arc fault?
Have been looking at AFDDs and can fit them (combined AFDD and RCBOs) on all the socket circuits in the house for circa £600, which seems a small price to pay to ensure that this fault didn't become more serious. However from what i can understand and AFDD wouldn't have picked this particular issue up as it occurred in series not parallel, which to be fair does seem like quite a blind stop for a £100 circuit breaker...
Am now also considering getting another EICR carried out and testing every socket in the house - would a multi meter be able to detect loose connections or will every socket have to be removed from the wall (i'm conscious that a couple are in very difficult to access locations?
1731329325333-png.118644
Hi Both
Just catching up on this.
If the sequence was you had an EICR which recommended a board change is there a chance the socket was disturbed during the EICR? The possibility increases if you say the other sockets are less accessible.
Of course it would be impossible to know for sure.
An EICR is a snap shot much like an MOT because the car passes on Monday doesn't necessarily say it would pass a week later.
Would be interesting to see the test results from the EIC of the board change to compare with the EICR. Again nothing would be conclusive but there is a chance because the circuits were tested say a week earlier they may or may not of used those results on the EIC? Assuming the same company did both the EICR and the Board change.
It is my understanding they will work with both series and parallel arc faults but watching David Saverys videos on these especially the Hager brand doesn't instill confidence.
It could be that the builders used that outlet for something like a cement mixer ?
It would have needed a fairly substantial load to cause that.
Hi and thanks
To answer queries:
1) Board change was at my request as the extra circuits required, inc for an A/C unit, required a secondary fuse board under the stairs so made sense to replace with one big enough for all new circuits and leaving expansion for EV charging etc in the future.
2) Therefore new board was installed first and then EICR done once all works complete. I don’t think an EIC was done on the old board before removing as plan was always to change.
3) Socket definitely not disturbed during testing as the decorators caulk around the edge was undisturbed until I removed the socket.
4) inaccessible sockets are behind a wardrobe upstairs and on the 1st floor sockets ring final
5) I did move a lamp, on a Tp-link smart plug to this socket in between testing and the socket burning out - perhaps just very unlucky that plugging something new into this socket disturbed a partly loose connection?
Afraid not - this room is at the front of the house where no works were done.
Only items plugged into this socket were a tplink smart plug with floor lamp connected, a four way extension cable with an Amazon fire stick and a deco m5 mesh router.
The radial circuit has two other sockets on it which had 1 table lamp, a 55” led tv, sky q box, a denon av receiver and a Panasonic surround sound subwoofer.
So nothing particularly load intense - worth getting some PAT testing done on those appliances?
Hi and thanks
To answer queries:
Ok Thanks for taking the time clearing all that up.
I don’t think a pat test is going to be very helpful.
Could it have had any substantial loads prior to what’s on it now such as a heater or dehumidifier.
This outlet isn’t end of line so I would have expected to see some intermittent failure of the other outlets.
Anyway I’m sure it will be fine now that the connections have been sorted.
Hi All
Alex
In the picture of the socket, it looks like one of the neutrals may have been screwed in over the insulation. Therefore, the live may also have been done in a similar way, which would loosen over time, and then with higher resistance would melt the insulation and quickly become much looser.
Reactions: Teddy Lop
Hi and thanks
To answer queries:
Who fitted the socket originally
Hi All
Hi All
Alex
Blame the poor sparky who changed the fuse board even though he never fitted the socket .I would think that it would result in a high resistance on continuity test but seen as its a radial maybe they thought this was a normal reading or maybe they only performed a efli test at last socket.i would put my hat on the problem being who ever fitted socket ,what do you have plugged in further down the line ,I see its lounge sockets and a radial..
I've seen a Japanese socket adapter with just a 7 watt led table lamp plugged in to it burn out the live pin in a single socket because it was so loose .it crackled when you touched the flex because it was such an ill fit
Alex
30 amp rcd certinaly wouldn't trip.sorry based on the photo it's a 30 ma rcbo .
Hi All
Alex
Was there rcd protection on that particular circuit previously
Hi All
Alex
Hey Alex!
It’s possible that the issue might be related to the new fuse board since it happened right after the change. Sometimes small changes in the electrical system can cause things that were fine before to start having issues. But like you mentioned, the socket was 10 years old with no issues. It could be that the live connection in the outlet burnt, but since this was a new setup, maybe something in the installation or connections changed, causing the socket to burn out. I’d recommend getting a professional electrician to check if everything is properly connected and there’s no issue with the new wiring.
Well spotted, and very true
Faults can have what I call a "cascade" effect, a mild fault - either a loose connection or a short, say from damaged insulation - can sit for years being a tiny little bit of a fault that goes un-noticed then as soon as a teeny increase occurs, perhaps just the gentle disturbance of plugging something in or using an extra appliance, it generates a tiny bit of heat, heat means more resistance, therefore more heat, more resistance etc and it quite quicky becomes a big fault.
Also notice decorating dust inside socket box, the very fine powdery dust from sanding filler by decorators too lazy to protect wiring accessories can get in all the switches, contacts etc and can cause things to not contact properly and arc.
Re: arc/heat faults and circuit protection; I remember reading something 20+ years ago where someone proposed fitting all sockets, switches etc with cheap thermal links between L-E, the idea being that if they were heated beyond their design spec they'd lower in resistance and pass enough current that the RCD would trip. Guess nothing came of it...
London
Advice on Burnt out wall socket
Alex Woodall,
Teddy Lop,