It needs to be extended only by about 30-40cm and junction box would be indoors about 30cm from the consumer unit in the houseif it can be hidden, just use a torpedo joint designed for being buried, with the resin.
Extend with same SWA.
Yes that would be acceptable if single insulated cables are going to be exposed then put them in some containment.I have run 10mm2 3 core SWA to garage CU but miscalculated the length and no way Im going to reach the house CU. I need to extend the cable, is it acceptable to do it like on the picture
Thanks of the idea, I will have an electrician replacing my house CU at some point next year, so will definitely consider this option. At the moment I am looking for a temporary solution (as simple and cost effective as possible) and wanted to know if the one I suggested is acceptable and safeWhat about taking the SWA to its own little CU and split the incoming tails with Henley blocks?
House CU can be isolated without affecting garage
I would definitely go for it but my CU in an old one with the back entry and no slots to gland SWA. I will do it properly when I replace the CU next year. Thank youYes that would be acceptable if single insulated cables are going to be exposed then put them in some containment.
A torpedo would probably be the easiest, even if you have to cut the feed cable back so that the join is in the best place.
It would also mean that the Swa can be glanded properly into the CU instead of having to use a junction box.
Thanks. Can I use 6181Y as earth if marked correctly?Just use some 10.0mm² 6181Y.
Just use some 10 mm earth cable.Thanks. Can I use 6181Y as earth if marked correctly?
Is 10mm² 3 Core HO7RNF suitable to be used instead of single insulated cables in a containment?Yes that would be acceptable if single insulated cables are going to be exposed then put them in some containment.
Yes that would be ok.Is 10mm² 3 Core HO7RNF suitable to be used instead of single insulated cables in a containment?
You would then need ferrules.Is 10mm² 3 Core HO7RNF suitable to be used instead of single insulated cables in a containment?
Thank youYes that would be ok.
The 6181Y wouldn't have to be in containment as they are double insulated.
I can get 1m of 3 Core HO7RNF and it is a bit tight behind the board so Id rather have one piece of cable and split it only at both ends. Thanks anyway for the adviceUse 6181Y a wholesaler will sell cut lengths including a cpc.
You will then need ferrules and a crimper.I can get 1m of 3 Core HO7RNF and it is a bit tight behind the board so Id rather have one piece of cable and split it only at both ends. Thanks anyway for the advice
Don’t you mean the RIGHT ferrules with the RIGHT crimper?You will then need ferrules and a crimper.
Do I have to use crimps? Can't I just use a terminal strips included in 57A JB and wire it as on the picture below?You will then need ferrules and a crimper.
Thanks, it worked well, but I have a problem. It turns out that the neutral terminal slots are too small for 10mm2 cable (it's an old CU). Can I run 6mm2 instead of 10mm2 from CU to junction box if I feed it from 30A MCB instead if 40A?Ferrules are used on multi strand conductors prior to termination to protect them.
YesThank you. I have another problem. It turns out that the neutral terminal slots are too small for 10mm2 cable (it's an old CU). Can I run 6mm2 instead of 10mm2 from CU to junction box if I feed it from 30A MCB instead if 40A?