You mean that you would have to switch on the entire circuit, with everything plugged in and switched on ready to go.

Does this happen often?
Or does it tend to coincide with periods of time when you have nothing useful to do?
You could have timed heaters plugged into the socket outlets in different rooms, all on the ring final set to come on at the same time.

I know of a few rental properties that have them, they replaced a 12kw electric central heating system that caused a fire in the one property.
 
Last edited:
You mean that you would have to switch on the entire circuit, with everything plugged in and switched on ready to go.

Not necessarily, a number of heaters could be used as the load.
Does this happen often?

Not very often in my experience, I can only recall seeing a ring circuit significantly overloaded when a heating system had failed and multiple heaters were plugged in.

Or does it tend to coincide with periods of time when you have nothing useful to do?

This seems like an entirely unnecessary comment
 
The question that remains unanswered is:
Do you agree that "making sure that the current carrying capacity of the smallest conductor in the circuit exceeds the I2 value of the chosen overcurrent protective device, is the 'easiest' way of protecting an electrical circuit against 'a small overload of a long duration'?
 
No I don't agree because I don't see how that would protect against such an overload as it would not stop such an overload from happening.
Using I2 to select a cable size would not change the In of the circuit or OCPD and so any such overload would happen exactly the same.
What it would do is reduce the temperature rise in the cable during such an overload, it would not change how anything else in the circuit is affected by the overload.

If it is necessary to protect against small overloads in a circuit then a protective device capable of offering such protection would be the answer.
 
The evidence suggests that you are correct about the temperature being the key, but experience has demonstrated that it will be the join between the line pin of the 13amp plug and the socket outlet where the point of ignition will be found.
 
If you choose a 32amp BS EN circuit breaker it should therefore be matched with a 4.0mm conductor ring final circuit and earthed metal-clad socket fronts.
 
The evidence suggests that you are correct about the temperature being the key, but experience has demonstrated that it will be the join between the line pin of the 13amp plug and the socket outlet where the point of ignition will be found.

Well you really have wandered off into the rhubarb now haven't you! You've jumped from discussing small overloads to points of ignition.

If there is ignition at a point such as you describe then it will be the result of an arc which can be protected against by an AFDD.

Changing the size of conductors will not do anything to help this new situation you have raised
 
  • Like
Reactions: DPG
If you choose a 32amp BS EN circuit breaker it should therefore be matched with a 4.0mm conductor ring final circuit and earthed metal-clad socket fronts.

Could you explain this please because, do far, you haven't provided anything to support this statement.

A standard ring final circuit can have 2.5mm conductors and the material that the socket is made from is irrelevant to the issue of overloads whether they be small, medium or large.
 
Why, that won't help your point at all.

Could you please just explain your point, make a well reasoned technical post so we can actually understand your point and then discuss it.

A statement that we just need to look at some photos of a disastrous fire which appears to have no relevance to your point is not helpful and doesn't explain anything.
 
  • Like
Reactions: DPG
A Faulty fridge freezer, a fuse then wrapped in silver paper, the point of ignition was the join between the 13amp plug and the socket outlet, a 32amp BS EN MCB in the 'ON' position, after the fire burned the insulation from the conductors, a short circuit then operated the RCD.
 
Teenagers understand the theory of continuity, therefore electricians must understand overcurrent protection.
Unless you plan to blame the childlike mind that wrapped the fuse in silver paper.
 