How do we protect an electrical circuit from 'a small overload of a long duration'?
 
Specify "long" and "small".
 
If the duration is sufficient for the over current protection to operate then that provides the protection.

We are required to design circuits to minimise the risk of small overloads affecting the circuit but also the current ratings given for cables etc have a tolerance built in to them to cope with small overloads that don't cause protective devices to operate.

If a more fine/precise protection than is afforded by standard over current protective devices is required for a particular application then additional protective devices can be installed, such as used in motor controls.
 
I can't argue with that.

Would you agree that the easiest way to achieve this would be; to make sure that the current carrying capacity of the smallest conductor within the circuit exceeds the I2 value of the chosen overcurrent protective device?
 
I don't have the time right now to give this much thought, I'll come back to it later.

It would be good if you could just tell us whatever it is you are leading up to with this rather than going through a drawn out process of baby-stepping towards it.

I am of course assuming, based on your previous contributions, that you are going to share with us an idea which contradicts current thinking and installation practices?
 
Give it some thought.
Perhaps somebody else might like to contribute whilst you are thinking.
 
  • Optimistic
Reactions: DPG
I have given it some thought and as it stands I am happy to accept the current position of using the 1.45 factor for circuit breakers and cartridge fuses.
As it stands I see no reason to go against this convention.

Perhaps you could offer up a well reasoned explanation as to why this may not be suitable?
 
  • Like
Reactions: DPG
Can a ring final circuit be subjected to 'a large overload of a short duration'?
 
Yes, of course it can, and the larger that overload is the shorter it's duration will be as the overload protection operates.
 
433.1 PROTECTION AGAINST OVERLOAD CURRENT
Coordination between conductor and overload protective device
Every circuit shall be designed so that a small overload of long duration is unlikely to occur.
 
How can a ring final circuit be exposed to 'a large overload of a short duration'?
 
How can a ring final circuit be exposed to 'a large overload of a short duration'?

Plugging in and operating an excessive number of high current appliances at the same time will create a large overload, the overload protective device will handle the short duration part.
 
  • Like
Reactions: mainline and DPG
You mean that you would have to switch on the entire circuit, with everything plugged in and switched on ready to go.

Does this happen often?
Or does it tend to coincide with periods of time when you have nothing useful to do?
 
You mean that you would have to switch on the entire circuit, with everything plugged in and switched on ready to go.

Does this happen often?
Or does it tend to coincide with periods of time when you have nothing useful to do?
You could have timed heaters plugged into the socket outlets in different rooms, all on the ring final set to come on at the same time.

I know of a few rental properties that have them, they replaced a 12kw electric central heating system that caused a fire in the one property.
 
Last edited:
You mean that you would have to switch on the entire circuit, with everything plugged in and switched on ready to go.

Not necessarily, a number of heaters could be used as the load.
Does this happen often?

Not very often in my experience, I can only recall seeing a ring circuit significantly overloaded when a heating system had failed and multiple heaters were plugged in.

Or does it tend to coincide with periods of time when you have nothing useful to do?

This seems like an entirely unnecessary comment
 
  • Like
Reactions: mainline and DPG
The question that remains unanswered is:
Do you agree that "making sure that the current carrying capacity of the smallest conductor in the circuit exceeds the I2 value of the chosen overcurrent protective device, is the 'easiest' way of protecting an electrical circuit against 'a small overload of a long duration'?
 
No I don't agree because I don't see how that would protect against such an overload as it would not stop such an overload from happening.
Using I2 to select a cable size would not change the In of the circuit or OCPD and so any such overload would happen exactly the same.
What it would do is reduce the temperature rise in the cable during such an overload, it would not change how anything else in the circuit is affected by the overload.

If it is necessary to protect against small overloads in a circuit then a protective device capable of offering such protection would be the answer.
 
I’m just going to say no
 
Last edited:
Status
Not open for further replies.

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Cheltenham
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Retired Electrician

Thread Information

Status
Not open for further replies.
Title
Overcurrent protection
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
56

Thread Tags

Tags Tags
protection

Advert

Thread statistics

Created
DWCOCKBURN,
Last reply from
littlespark,
Replies
56
Views
864

Advert