Hello I have been asked to assist in fault finding on the above refrigeration compressor the unit is wired as a part winding 20 HP 3 phase 415 volt 32 amp run current with an approximate starting current of 98 amps.
This is supplied from a 31KVA Stanford Genset.
The 50 amp “Schneider NSX100B with a TM 50 D overcurrent trip mech” there is also a “Mikro IDT overcurrent relay NX204A in the protection circuit”, Genset circuit breaker tips at a measure inrush of approximately 65 amps,
I believe the Genset has been wrongly sized any assistance will be appreciated
Cheers Trumby