I have had a extention built on existing kitchen and had kitchen and extention off a new consumer unit. (I didnt do electrics was all in either builders quotes). I have a intergrated oven on a switch which is 32a from C/u. But i have a 16a Combination oven that the electrician has fitted on a 13a fused spur off the Ring I would of said needs 16a direct from C/u like the 32a oven But electrician tried to say due to 16a being maximum and diversity rule 13a spur would be fine and if was worried he would change to 20a double pole switch


Please advise
 

Attachments

  • IMG_4792.jpeg
    IMG_4792.jpeg
    718.7 KB · Views: 38
Is that flex just coming through a hole in the wall? I don’t think it’ll have any strain relief.

Should have been a switch with an outlet, or a separate outlet controlled by the switch.

As for the 13A spur, I would use a 20A switch, more for the fact that it would be a double pole isolation, whereas the switch fuse may or may not be DP.

Check what the manufacturers instructions state for connection.
If it was designed for 13A, or might have come with a plug on it…
 
Is that flex just coming through a hole in the wall? I don’t think it’ll have any strain relief.

Should have been a switch with an outlet, or a separate outlet controlled by the switch.

As for the 13A spur, I would use a 20A switch, more for the fact that it would be a double pole isolation, whereas the switch fuse may or may not be DP.

Check what the manufacturers instructions state for connection.
If it was designed for 13A, or might have come with a plug on it…
The flex is the 32a cooker installed into switch which is direct to 32a breaker at c/u the rhs one the 13a spur is not in atm has i took out as wasnt happy that it states in manufacturer instructions 16a. But thats a 13a
 
MIs suggest that it came with a plug that should be plugged into an accessible socket if possible, but a socket through an accessible isolating switch if the socket is not accessible. They then go on to say it can be directly connected without a plug and socket, so basically do as you like.
However, the product specification does say to be fused at 16A, which, of course, isn't compatible with the plug being a UK one with a 13A fuse maximum.
There's also the matter of fixed appliances <2kW connected to a RFC.
If I'd done the job, it would have been wired directly back to a 16A RCBO in the new CU, with a 20A accessible switch near the appliance, but this smacks of a sparks subbing to a builder and trying to maximise his profits.
 
MIs suggest that it came with a plug that should be plugged into an accessible socket if possible, but a socket through an accessible isolating switch if the socket is not accessible. They then go on to say it can be directly connected without a plug and socket, so basically do as you like.
However, the product specification does say to be fused at 16A, which, of course, isn't compatible with the plug being a UK one with a 13A fuse maximum.
There's also the matter of fixed appliances <2kW connected to a RFC.
If I'd done the job, it would have been wired directly back to a 16A RCBO in the new CU, with a 20A accessible switch near the appliance, but this smacks of a sparks subbing to a builder and trying to maximise his profits.
It didnt come with a plug. Just the flex cable. Electrician has said he will change the 13a fused spur for a 20amp double pole isolator. Could you tell me if this is safe or what dangers there is has im going to just get done correctly if hes going to bodge it
 