Hi all.
It has been a long time since I have been on this site asking for advice on central heating controls. But, I now do need some help if possible. I installed a tado v3+ starter kit a little over a yr ago. 3 weeks ago the client called me to tell me the heating wouldn't turn off. I inspected the receiver which seem to be continuously calling for heating without demand. Called Tado and they sent me a new one. 3 weeks later the same fault.
Now Tado have said I need to install a relay to stop the contacts in the receiver welding together when the pump turns on. Now I have installed a few tado controls and never experienced this. They have sent me a diagram of the relay and the wiring, but for the life of me I cannot figure out how to wire this up. Ideally I want it in the airing cupboard with the wiring centre and pump etc (the receiver that is welding is in the kitchen).
Please see the image attached from Tado and one i found on the relay manufacturers website.
The system is a Y plan. Do I take

Do I take a live and neutral from the wiring centre to A1 and A2 on the relay and then CHNO to 13 on the relay and then 14 on the relay to white wire on the 3 port to switch the pump or do I take it to the orange wire after the valve has switched?
Thanks again if anyone has any advice.
Mutts
It has been a long time since I have been on this site asking for advice on central heating controls. But, I now do need some help if possible. I installed a tado v3+ starter kit a little over a yr ago. 3 weeks ago the client called me to tell me the heating wouldn't turn off. I inspected the receiver which seem to be continuously calling for heating without demand. Called Tado and they sent me a new one. 3 weeks later the same fault.
Now Tado have said I need to install a relay to stop the contacts in the receiver welding together when the pump turns on. Now I have installed a few tado controls and never experienced this. They have sent me a diagram of the relay and the wiring, but for the life of me I cannot figure out how to wire this up. Ideally I want it in the airing cupboard with the wiring centre and pump etc (the receiver that is welding is in the kitchen).
Please see the image attached from Tado and one i found on the relay manufacturers website.
The system is a Y plan. Do I take


Do I take a live and neutral from the wiring centre to A1 and A2 on the relay and then CHNO to 13 on the relay and then 14 on the relay to white wire on the 3 port to switch the pump or do I take it to the orange wire after the valve has switched?
Thanks again if anyone has any advice.
Mutts